Insurer declined new internal flooring and external concrete damage after a leaking pipe claim, attributing it to property condition or gradual deterioration
Text of the determination
Determination
|
Case number
|
12-25-336106
|
Financial firm
|
Auto & General Services Pty Ltd
Case number: 12-25-336106 31 August 2026
1 Determination overview
1.1 Complaint
The complainant holds a home and contents policy with the financial firm (insurer).
In May 2024 the complainant lodged a claim for damage caused by a leaking pipe under concrete at the property. Although the insurer initially accepted the claim, it later declined new damage to the internal flooring and external concrete paths on the basis that the condition of the property, or gradual deterioration, was the cause of the damage, and not the leaking pipe.
The complainant says the insurer should have completed drying, and restoration works to prevent further damage. He seeks cover for all damage caused by the leaking pipe.
1.2 Issues and key findings
Did the insurer correctly assess the claim?
No. The insurer must accept the internal damage to the building under the claim as it was caused by the leaking pipe. The insurer is not required to accept the cracking damage to the exterior concrete as the information shows it was not caused by the leaking pipe.
Is the complainant entitled to compensation for non-financial loss?
Yes. The complainant is entitled to $1,000 in compensation because the insurer’s claim handling caused undue stress and inconvenience.
Why is the outcome fair?
The outcome is fair because the exchanged information shows that not all the claimed damage was caused by the leaking pipe. It would not be fair for the insurer to pay for damage that is not covered by the policy.
However, where the insurer has not established an exclusion applies, it is fair that it provides cover for certain items under the claim.
1.3 Determination
This determination is in favour of the complainant.
If the complainant accepts the determination, within 14 days of being notified of his acceptance, the insurer must:
· pay $1,000 in compensation for non-financial loss
· reimburse the complainant for the fair and reasonable cost of repairing the flooring and other internal damage, and for reasonable temporary accommodation costs, based on the invoices he provided, less any amount the insurer has already paid for that damage.
· The insurer must also pay interest on the cash settlement amount under section 57 of the Insurance Contracts Act 1984 (Cth) (the Act). Interest is payable from the date the complainant paid the invoice, to the date the insurer issues the payment.
2 Reasons for determination
2.1 Did the insurer correctly assess the claim?
No. The insurer must accept the internal damage to the building under the claim as it was caused by the leaking pipe. The insurer is not required to accept the cracking damage to the patio as the information shows it was not caused by the leaking pipe.
Complainant must establish claimable loss
When making a claim, the complainant must first establish they suffered a loss covered by their insurance policy. The insured party must establish this on the balance of probabilities, meaning it is more likely than not.
If the complainant establishes a claimable loss, the insurer must show, on the balance of probabilities, the application of any exclusion it relies on to reduce its liability.
Policy covers damage caused by escape of liquid
The policy coverage is set out in the certificate of insurance and the product disclosure statement (PDS). Relevant policy terms are quoted in section 3.2 of this determination.
The policy is an ‘insured events’ policy. This means not all loss and damage is automatically covered. Rather, only loss or damage caused by one or more of the insured events, and not subject to exclusions, is covered. One of the insured events is Escape of Liquid.
The insurer offers optional additional cover for accidental damage, but the complainant’s policy does not include this cover.
To establish a claimable loss under the policy, the complainant must show the damage claimed is due to water leaking from one of the items listed in the ‘escape of liquid’ section, including a fixed pipe.
Proximate cause of the damage must be established
The proximate cause of a loss is the dominant, effective or operative cause. It does not have to be the first, the last or the sole cause. This is a question of fact depending on the circumstances.
If there are several causes, each needs to be examined to identify the proximate cause. For example, if one cause would have caused the loss in any event, and another cause would not have done so without the first, then the first is the proximate cause.
The exchanged information shows that the leaking pipe caused additional damage
I have considered the information exchanged. The key extracts from the reports supplied by the parties are set out in section 3.3.
The insurer mainly relies on reports from EC, an engineer who first inspected the site 18 months after the leak was repaired.
In October 2024, the insurer accepted and cash settled resulting building damage from the leaking pipe based on a scope of works totalling $24,645.72. The complainant reported new damage in June 2025.
In my view, the leaking pipe was the proximate cause of the additional flooring and wall lining damage. I find this because:
· There is no information that shows the flooring was already damaged or that the subfloor conditions were causing moisture issues at the home before the leak was identified.
· All of the insurer’s reports identify poor subfloor ventilation and generally agree that damage caused by cupping of the floorboards, and to wall linings, skirting and architraves resulted from damp subfloor conditions.
· The insurer’s appointed builder and internal assessor reported in 2024 and 2025 that the leaking pipe had contributed to or caused building damage. The insurer accepted and cash settled damage to wall linings, architraves and skirting in the hall, main bedroom, office and kitchen.
· The complainant’s expert, EF, reported that the concealed leak caused the observed damage through a chain of events involving saturated clay soil. He noted the leaking pipe was discovered only after internal wall damage was identified, and that the walls were now shifting to the touch. EF said drying works should have been completed but were not.
· The insurer appointed an engineer, EC, who provided several reports. EC found that the leaking pipe caused no damage and that the building’s inherent conditions caused the floorboards to cup. I give less weight to EC’s opinion because it does not sufficiently address the extent or duration of the concealed leak or explain why the internal damage worsened after the leak.
· EC also accepts that the subfloor can retain moisture over time. This reduces the persuasiveness of its view that the leak did not cause the damage because it was identified 20 months before EC’s inspection and the soil should have dried by then.
I accept that the subfloor does not meet current standards in relation to clearance and ventilation and is prone to retaining moisture. However, based on the information exchanged, the leak was concealed and prolonged. Based on the insurer’s initial acceptance, and the lack of persuasive reasoning to the contrary, I am satisfied the leaking pipe was the dominant cause of the internal damage.
I am therefore satisfied the complainant has shown escape of liquid was the proximate cause of the additional internal flooring damage. Accordingly, the insurer must accept that part of the claim unless it can establish a relevant exclusion.
Insurer has not shown any exclusion applies to internal building damage
The insurer has noted the policy generally excludes cover for damage caused by certain factors, including:
· The house is not in good condition
· Gradual deterioration over time
· Earth movement
The insurer has not shown that gradual deterioration, including mould or rising damp, caused the damage. As I am satisfied that the leaking pipe caused the damage, the resulting mould and rising damp were effects, not causes.
Similarly, the earlier assessments attributed the observed building damage and movement to the leaking pipe. This means ground movement was also an effect of the leaking pipe, not the cause of it.
I acknowledge that the damage worsened over time and the subfloor clearance is less than that required by current building standards. However, I am more persuaded that, without the leaking pipe, the property’s condition would not have caused the loss. The insurer has also not specifically explained how it was prejudiced by the unrepaired damage, or the property’s condition after the event.
I am not satisfied the insurer has shown an exclusion applies to defeat the claim for damage.
The complainant says he has now completed the relevant works. The insurer must therefore accept the claim for the additional internal building damage. It must reimburse the complainant’s fair and reasonable repair costs, less the amount it has already paid for that damage, in accordance with the policy terms.
The insurer must also reimburse reasonable temporary accommodation costs incurred during the repair period.
The leaking pipe did not cause the damage to the front porch concrete slab
The complainant has also claimed for damage to the front porch concrete which he says is cracking due to the escape of liquid event.
The insurer assessed this damage and found that structural defects caused the damage. It identified inadequate membrane support, which resulted in gradual cracking and deterioration.
EC also noted that cracks on the porch had previously been painted over and patch repaired indicating the cracking damage had been ongoing for some time.
The complainant’s expert said the cracking was due to soil saturation. However, based on the images and commentary supplied by EC and the insurer’s assessor, I am satisfied the cracking damage occurred gradually over time.
The exchanged information does not show, on balance, the escape of liquid or any other insured event caused the damage claimed.
I am satisfied that the complainant has not established a claimable loss, and the insurer is entitled to decline to cover damage to the concrete.
2.2 Is the complainant entitled to compensation for his claim experience?
Yes. I am satisfied the insurer’s claim handling caused the complainant an unusual degree of stress and inconvenience.
AFCA can award compensation for non-financial loss
Under the AFCA Rules, AFCA may award non-financial loss compensation, capped at $6,300, where a complainant has suffered an unusual degree of physical inconvenience, time taken to resolve the situation, or interference with their enjoyment or peace of mind.
Complainants should be aware that compensation for non-financial loss is not awarded where a person experiences the normal degree of inconvenience when a problem occurs. Non-financial loss compensation is also not intended to be a punishment for any wrongdoing by the insurer.
The insurer’s claim handling involved delays and errors
The complainant seeks compensation for his claim experience. He has provided medical information showing that he had medical attendances for himself and his infant son. He also says the claim caused significant disruption for him and his family.
I consider compensation for non-financial loss is fair because:
· The insurer reopened the claim in July 2025 but, after offering a cash settlement, decided it needed to appoint an engineer. This caused a delay in the assessment of the claim.
· The claim required several site attendances, including two engineering inspections. The insurer may have avoided multiple attendances if it had clearly defined the scope of the engineering review from the outset. In particular, the engineer appears to have reattended to address the subfloor, which should have formed part of the initial assessment.
· The time taken to reach an outcome prolonged the uncertainty for the complainant and his family while they remained in a home with high moisture levels.
The insurer has previously awarded the complainant $3,000 in compensation. I have considered this when assessing the overall impact of the claim on the complainant and the fair amount of compensation.
I am satisfied it is fair to award a further $1,000 compensation in the circumstances.
2.3 Why is the outcome fair?
The outcome is fair because the exchanged information shows that not all the claimed damage was caused by the leaking pipe. It would not be fair for the insurer to pay for damage that is not covered by the policy.
However, where the insurer has not established an exclusion applies, it is fair that it provides cover for certain items under the claim.
3 Supporting information
3.1 The AFCA process
AFCA’s approach is based on fairness
AFCA has determined this complaint based on what is fair in all the circumstances, having regard to:
· the legal principles
· applicable industry codes or guidance
· good industry practice
· previous decisions of AFCA or its predecessor schemes, which are not binding.
The parties have completed a full exchange of the relevant information, and each party has had the opportunity to address any issues raised. We have reviewed and considered all the information the parties provided.
While the parties have raised a number of issues in their submissions, we have restricted this determination to the issues that are relevant to the outcome.
We assess complaints on available information and circumstances
AFCA is not a court of law. We do not have the power to take or test evidence on oath, or to require third parties to give evidence.
When we assess complaints, we consider:
· available documents
· the recollections of the parties
· all relevant circumstances.
We give more weight to documents created at the time the events occurred. If there are no relevant documents, we will decide what most likely occurred based on the available information.
If there are conflicting recollections and these are evenly weighted, we may find that a claim cannot be established.
3.2 Product Disclosure Statement
Escape of liquid
You are covered for
Loss or damage at the insured address caused by the sudden escape of liquid.
You are also covered for damage from liquid that has escaped slowly over time that you couldn’t be reasonably aware of.
You are covered for loss or damage caused by the escape of liquid from the following list of things:
…
l fixed items: limited to baths, sinks, toilets, basins, other fixed plumbing apparatus, pipes, taps, gutters, and drainpipes
l fixed systems: limited to drainage or sewage systems, heating or cooling systems, or sealed portable units or tanks
…
Earth movement
You are not covered for loss, damage, or any legal liability you incur caused by any earth movement.
Earth movement you could be covered for
If you have Home or Contents Insurance, we will cover loss or damage caused by earth movement that occurs within 72 hours and as a direct result of the following insured events:
l Earthquake or tsunami
l Explosion
Gradual deterioration
You are not covered for loss or damage caused by any gradual deterioration to the extent that the gradual deterioration contributed to or caused the loss or damage.
Some examples of gradual deterioration are things like rust, corrosion, rot, mould, rising damp, mildew, wear, tear, or fading.
When your claim involves gradual deterioration
We will not repair or replace parts of your home or contents that have suffered loss or damage as a result of gradual deterioration. In the instance where there are multiple causes or areas of loss or damage to your home or contents, we will cover the part of the loss or damage caused by an insured event or optional cover.
Not in good condition
You are not covered for loss or damage you incur because:
l you have not kept the home or contents in good condition, or
l existing defects or faults contributed to or caused the loss or damage, or
l you have not done building work to the home requested by a relevant authority before the loss or damage occurred.
3.3 Report extracts
|
Record
|
Key points
|
Financial firm’s builder RP Report
19 June 2024
|
Insured has advised that he had noticed water patches to some walls throughout the property. He engaged a plumber and it appears that there was a leaking pipe which has since been repaired.
There are signs of possible rising damp issues which could be contributing to the damage. I noted a lack of subfloor access and would not achieve the minimum clearance of 450mm between the ground and internal floor.
…
It was mentioned that the damages occurred due to the burst water pipe leaking beside the property for an unknown timeframe. However, our technician believes there are subfloor ventilation concerns as the property is low to the ground with no brick vents minimal subfloor ventilation and rising damp issues.
|
Insurer’s assessment report
Report
11 July 2025
|
HA & BA concluded the following:
- The property has a strong musty odour, consistent with high moisture levels & rising damp.
…
- Due to the lack of sub-floor mechanical ventilation, rising damp has continued to damage the timber flooring throughout the property.
- Continued rising damp issues may have been caused by the previous EOL event, possible storm-water ingress through sub-floor vents, possible water ingress from A/C outlet directed onto the external wall, and possible water ingress from poor roof maintenance.
- Due to multiple contributing factors of water ingress, HA & BA could not exclude the EOL event that occurred on 11 May 2024, which may have contributed to continued rising damp issues and further damage to the timber flooring.
- Insured has been cash settled for repairs for remove/replace plasterboard wall linings & skirtings, painting of all walls.
- RPF cannot warrant repairs to the damaged timber flooring, due to non-compliance of sub-floor clearance height and continued possibility of rising damp, due to the insured’s lack of professional roof maintenance & minimal sub-floor ventilation, which requires constant mechanical ventilation.
- Insured to be cash settled for replacement of water damaged (cupped) timber flooring in bedrooms 1 & 2, hallway & living room.
…
*Resulting damage; rising damp water damage to timber flooring in bedrooms, living room & hallway.
- Repairs include remove/replace solid timber flooring, floor joists & bearers.
…
|
Internal assessor report (cracking to patio concrete slab)
Report
11 July 2025
|
The patio slab deterioration is consistent with long-term structural defect and natural ageing, occurring progressively over a century. The slab was constructed without proper footing support or membrane protection, resulting in gradual cracking and deterioration. The recently installed hard surface areas may
have accelerated water runoff and contributed to subsoil dampness. However, this is a maintenance and design issue rather than damage caused by a single insurable event.
|
Report of ECW
Complainant’s builder
23 August 2025
|
It is evident that sections of the veranda have subsided due to excessive water ingress within the underlying substrate. The presence of a leaking water pipe in close proximity has contributed to the deterioration of the concrete slab by oversaturating the subgrade.
|
Report EC,
Insurer’s engineer
8 October 2025
|
Cupping of the floorboards typically occurs as a result of moisture related issues. This happens when the underside of the timber absorbs more moisture than the top surface, causing the boards to expand unevenly and curve upward along the edges. In this
case, cupping was observed consistently across the floorboards throughout the dwelling, rather than being confined to the area of leaked pipe. Moisture readings taken during the inspection also showed elevated levels throughout the property, which is commonly seen in older dwellings due to inadequate subfloor ventilation and poor site drainage.
Evidence from the site inspection indicates that the issues are inherent due to the construction type and are widespread throughout the dwelling and are not confined to
the area near to the leaking pipe.
…
Our inspection noted cupping of the floorboards consistently throughout the dwelling, along with gaps between the floorboards and skirting. The consistent issues are not confined to the area near the leaking pipe indicating a longer-term issue related to
subfloor ventilation and seasonal movement.
|
Report EC,
27 November 2025
|
This construction condition creates an environment where humidity consistently remains elevated, especially following periods of rain or during naturally humid weather. Over time, this trapped moisture leads to the gradual development of mould,
fungal staining, and general dampness across timber surfaces and soil. These effects occur even in the absence of leaks, simply as a consequence of prolonged exposure to a poorly ventilated and moisture-rich subfloor environment.
The underlying and primary cause of the mould observed, which is likely to be consistent throughout the entire subfloor area, is the long-term environmental conditions created by the original construction being so close to ground level. The minimal clearance restricts ventilation, allowing moisture to accumulate and persist, which in turn promotes mould growth and moisture staining on surrounding materials.
…
Initial drying works undertaken in the subfloor would not necessarily have resulted in any lasting improvement to its condition. The fundamental issue lies not with the short-term presence of moisture from a leak, but with the inherent construction and environmental characteristics of the subfloor itself. If drying equipment was installed, it would have been capable of extracting moisture from the immediate environment, including drawing moisture from the surface layers of the soil. While this would reduce humidity levels for the duration of the works, it would not address the underlying causes, namely low clearance and poor ventilation. As soon as the drying equipment was removed, the subfloor conditions would return to their natural equilibrium. Humidity would increase again due to the lack of airflow, and mould growth would continue or re-emerge over time.
The evidence indicates that the subfloor would inevitably revert to the same damp, humid conditions observed, regardless of any temporary drying attempts.
…
Given the original construction of the dwelling, any initial subfloor drying would not have provided lasting improvement to the condition of the subfloor. Due to low clearance and poor ventilation, the space naturally retains humidity, allowing mould to
develop. Any moisture removed during drying would return once equipment was removed, causing the subfloor to revert to its original damp, humid condition over time, regardless of any pipe leak.
|
Complainant’s expert
EF Report
11 December 2025
|
Attended site and inspected damaged areas. Took moisture readings of walls and floating floors where listed above….
OPINION:
This damage has been caused by an outside leaking pipe that was concealed under the concrete, with the waters entry through the external wall and into and onto the concrete subfloor. It then soaked up the gyprock walls, and into the floating floors. This has been leaking for some time judging by the moisture readings.
In our opinion, the damage has been exacerbated by the following:
1) The ground under the leaking pipe is clay which holds moisture. This caused a chain of events. The external walls were eventually soaked by the still leaking pipe and the saturated clay. The water then soaked through the wall to inside the house where it pooled on and in the concrete subfloor. Water sitting on top of the subfloor caused the floating floor to cup and buckle.
2) We were told by the owner that representatives for the insurance company attended the site, but did not take any steps to remediate the water problem. Air movers and dehumidifiers should have been installed to remove moisture from the air and begin to dry the walls and floors as soon as possible.
However, according to the owner, this was not done.
3) In our opinion, this allowed the damage to the floating floors and parts of the walls to reach such a level that the floating floors now need to be totally removed and replaced, and the walls will need to be cut to allow drying in the wall cavities, the house frame, the joists and trusses.
|
Supplementary report, EC
17 Feb 2026
|
While the insured’s moisture specialist has attributed the observed deterioration primarily to the pipe leak and subsequent lack of drying, this conclusion does not adequately consider the inherent subfloor construction conditions that pre-date, and continue independent of, the leak event.
The subfloor clearance is minimal, with the underside of the floor constructed very close to ground level. Subfloors built with such restricted clearance are well recognised as being highly susceptible to persistent moisture retention, elevated humidity, and limited air circulation. Where airflow is constrained, ground moisture cannot dissipate effectively, resulting in a consistently damp and humid environment. Over time, these environmental conditions promote mould growth, fungal staining, and general moisture-related deterioration to timber elements, even in the absence of any plumbing leak.
The primary and underlying cause of the mould and dampness observed is therefore the long-term environmental condition created by inadequate subfloor ventilation and insufficient clearance from ground level. These conditions would have existed prior to the pipe leak and, notably, remain present 18 months after the leak was repaired.
Coded fields were extracted from the text by a language model and may contain errors. The published PDF is the authoritative record.