Home / Chubb / Determination 12-25-332061
Determination 12-25-332061
Claim declined for collapse of parapet wall; insurer relied on defective design/construction exclusion
Summary
An owners corporation claimed for a collapsed parapet wall it attributed to storm; the insurer declined, citing the defective design/construction exclusion. AFCA found in favour of the insurer.
On expert evidence, the dominant cause of collapse was the wall's inadequate design/construction rather than the storm, so the policy exclusion applied and the resultant-damage exception did not cover the wall itself.
Issues
- Claim denial primary · not upheld“The insurer is entitled to decline the claim; proximate cause was defective design and construction, excluded under the policy.”
- Inadequate claim investigation secondary · not upheld“Fair for insurer to rely on its engineers' reports where complainant provided no conflicting expert evidence.”
- Product terms interpretation secondary · not upheld“Exception covers only resultant damage, not the defective wall itself; insurer's interpretation of exclusion is fair.”
Subjects and remedies
broker or intermediaryhome or building damageno remedy
Related
Text of the determination
Determination
|
Case number
|
12-25-332061
|
Financial firm
|
Chubb Insurance Australia Ltd
Case number: 12-25-332061 22 September 2026
1 Determination overview
1.1 Complaint
The complainant is the Owner’s Corporation (OC) of a residential strata insurance policy (policy) held with the financial firm (insurer). The OC is represented by its appointed broker. Reference to the complainant in this determination includes both the broker and the complainant unless specified otherwise.
On 2 July 2025, a claim was lodged for the collapse of a parapet block wall (wall) above roof level on the western boundary of the insured building. The complainant says the damage is due to high wind speeds (storm damage) the previous day on 1 July 2025.
The insurer has declined the claim. It says the dominant cause for the wall damage is not storm. Rather, that the damage is due to defective design, materials and/or workmanship, which is excluded under the policy.
The complainant disputes the insurer’s assessment of the proximate cause for the damage. Also, the complainant says it was unaware of any such defect and the insurer’s interpretation of and therefore reliance on the policy exclusion is unreasonable.
1.2 Issues and key findings
Has the complainant established a valid claim?
Yes. The policy covers the insured building against sudden and unforeseen physical loss or damage due to an occurrence or accident.
Is the insurer’s assessment of its liability under the policy reasonable?
Yes. The exchanged information supports the insurer’s position that the proximate cause for the damage relates to the defective design/construction of the wall. Loss or damage in these circumstances is excluded under the policy.
Why is the outcome fair?
The outcome is fair as it is based on the exchanged information and the policy. The exchanged information shows it is more likely than not that the wall collapsed due to factors excluded under the policy. It would be unfair to require the insurer to accept liability for the damage where it is otherwise not required to under the policy.
1.3 Determination
This determination is in favour of the insurer.
The insurer is entitled to decline the claim and is not required to take any further action.
2 Reasons for determination
2.1 Has the complainant established a valid claim?
Yes. The policy covers the insured building against sudden and unforeseen physical loss or damage due to an occurrence or accident.
The policy covers the insured building against accidental loss or damage
The insurer provided the complainant with the relevant policy documentation including the product disclosure statement (PDS) and certificate of insurance (COI). I accept the insurer is entitled to rely on the policy provisions to assess its liability under the claim.
The policy covers the insured building against accidental loss or damage. Cover under the policy is subject to the conditions, limitations and exclusions specified in the PDS.
Complainant has onus to show the damage triggers cover under the policy
When making a claim, the complainant has the initial onus of establishing it suffered a loss for which the insurance policy provides cover. The complainant must establish this on the balance of probabilities (i.e. that it is more likely than not).
If a claimable loss is established, the insurer has the onus of establishing, on balance, the application of any exclusion it relies on to reduce its liability or deny the claim.
This means that not all loss and damage is automatically covered. Rather, cover is limited to physical damage due to an event that occurs during the period of insurance and is not otherwise excluded.
The policy defines the term ‘Event’ as an occurrence or accident resulting in sudden and unforeseen physical loss or destruction to the insured building.
The relevant policy wording is provided in section 3.2 below.
The building has suffered physical loss or destruction
There is no dispute the wall collapsed on 1 July 2025 during the storm. Further, that the collapse was sudden and was not reasonably foreseeable from the complainant’s point of view. That is, there is no evidence to show the complainant was reasonably aware of any issues or defects with the wall prior to its collapse.
Given this, and the broad form accidental loss or damage policy, I am satisfied it is fair to accept the complainant has established a valid claim. Cover under the policy remains subject to limitations, conditions and exclusions specified in the policy.
The onus rests with the insurer to show, on balance, an entitlement to decline the claim in line with the policy or otherwise.
2.2 Is the insurer’s assessment of its liability reasonable?
Yes. The exchanged information supports the insurer’s position that the proximate cause for the damage relates to the defective design/construction of the wall. Loss or damage in these circumstances is excluded under the policy.
Parties have opposing views regarding policy response to the damage
The complainant believes the insurer is liable for the claimed damage in line with the policy. The complainant says:
· the insurer has not reasonably considered the actual wind speed, direction or duration of the storm in the exact location of the insured building
· the insurer has not considered the fact the wall had remained in place for 30 years
· the insurer relies on theoretical numbers/estimates for design wind speeds/pressures/loads
· the insurer relies on guesses and assumptions in forming its view on the cause of the wall collapse
· the insurer relies on the ultimate limit state design load, not the expected serviceability or operation condition that a typical boundary wall would be designed to resist, particularly when built in the 1990’s
· the insurer fails to recognise and/or has misinterpreted an exception to the policy exclusion where it cannot refuse a claim where the complainant could not reasonably have been aware of the defect.
The insurer accepts the complainant may not have been aware of the inherent issues with the wall’s construction. Also, that the exception to the relevant policy exclusion would allow cover for any resultant damage from the collapsed wall. However, the insurer says there is no resultant damage and the wall being the faulty item itself is not considered resultant damage.
The insurer relies on reports from its appointed engineering consultants ‘S’ to maintain the damage to the wall is due to defective design/construction. S describes the design of the wall as ‘grossly inadequate’ and not consistent with the relevant building standards in place at the time of its construction. Given this, the insurer maintains its decision to decline the claim for the damaged wall.
AFCA’s approach to proximate cause
The proximate cause of a loss is the dominant, effective or operative cause. It does not have to be the first, the last or the sole cause. This is a question of fact depending on the circumstances.
If there are several causes, each needs to be examined for qualities of reality, predominance and efficiency to identify the proximate cause. For example, if one cause would have caused the loss in any case, and the other one would not have done so without the first, then the first is the proximate cause.
Information from the insurer’s expert is persuasive
The insurer appointed engineering consultants S to investigate the cause and extent of the damage to the wall. S attended the insured property on 21 July 2025 to complete its assessment of the cause and extent of the damage. S has provided two reports dated 4 August 2025 and 25 March 2026.
S’s review of data from the Bureau of Meteorology (BoM) shows maximum wind gusts of approximately 83 km/h to 85 km/h around the claimed date of loss. S also identified similar wind speeds in the months before the wall’s collapse. Based on historical wind data S says the wind event on 1 July 2025 was not unusual enough, by itself, to explain the damage to the wall.
S’s report dated 4 August 2025 compared the recorded wind gusts with the design wind speed said to apply at the time of construction. It initially referred to a design wind speed of about 169 km/h. S says the wall should have been able to withstand a much higher design wind load than the wind experienced on 1 July 2025. S concluded the damage was more likely caused by inherent design inadequacies, rather than a one-off storm event.
I note in its supplementary report dated 25 March 2026, S has provided more detailed reasoning about the standards and calculations relevant to the wall’s construction. S has explained there was no automatic requirement for every masonry wall to contain reinforcement. However, the wall still had to be designed so it would not overturn under the applicable wind loads. S refers to Australian Standards (AS) AS 3700-1988 and AS 1170.2-1989 as the relevant standards at the time of construction.
In the supplementary report, S has recalculated the relevant design wind speed to be 104.6 km/h, and that this was based on assumptions more favourable to the complainant. I note this is lower than the 169 km/h figure referred to S’s the first report. Regardless, it remains higher than the 83-85 km/h wind speeds recorded on the date of loss.
The supplementary report considers the wall’s ability to resist overturning. S estimates that the wind load created an overturning moment of 1.01 kNm per metre. The wall’s own weight provided a stabilising moment of only 0.28 kNm per metre. This means the overturning force was about 3.6 times greater than the wall’s available resistance.
S concludes that, without reinforcement, engaged piers, or another stabilising system, the wall did not have enough capacity to resist the applicable wind loads.
Overall S finds that the wall collapsed because it was structurally inadequate for the wind loads it should have been designed to resist. The wind on 1 July 2025 exposed the pre-existing design/construction weakness in the wall. That is, it had insufficient resistance to lateral wind loading and overturning.
The complainant has not provided any expert evidence in support of its position regarding the damage to the wall or contrary to the insurer’s appointed experts.
Storm has not been established as the proximate cause for the damage
I acknowledge the complainant has raised several concerns regarding S’s assessment and findings. However, there is no evidence of these concerns being based on the opinion of a suitably qualified expert. The complainant has not provided any qualified and independent conflicting expert evidence for consideration.
Without such expert evidence to the contrary, I accept it is fair for the insurer to rely on the opinions of its appointed expert. Further, that it would be unreasonable to simply disregard the expert reports in the absence of any qualified evidence to the contrary.
I accept S’s position that the proximate cause for the wall’s collapse was not the storm event on 1 July 2025. In reviewing proximate cause, I have considered the real, effective and dominant cause of the damage, rather than only the storm event that immediately preceded the collapse. On the available evidence, the wall collapsed during the storm, but it was not the dominant cause of that failure.
I acknowledge there were 83-85 km/h wind speeds on the date of loss. Further, that in line with the Beaufort Wind Scale, such wind speeds are classed as a ‘Strong gale’ event with the potential to cause light structural damage. However, I am not satisfied the collapse of the wall can reasonably be considered light structural damage.
I also note the exchanged information shows the relevant location has in the past experienced similar and stronger wind speed events. That is, this event on 1 July 2025 was not unique. I accept the expert’s view that had wind speeds alone been the dominant cause, it is most likely the wall would have collapsed in previous similar conditions. The complainant’s information concedes it is likely the wall has been weakened over time due to exposure to weather events over the years.
I accept S’s evidence is persuasive in identifying it is most likely the wall had pre-existing structural weakness. This is because the wall was unreinforced, hollow, and effectively freestanding. The wall mainly relied on its own weight to resist lateral wind forces. Evidence from S explains that, even on assumptions favourable to the insured, the applicable design wind speed was 104.6 km/h. This being materially higher than the wind speed recorded on the date of loss.
S’s report also calculates that the overturning moment exceeded the stabilising moment provided by the wall’s own weight by about 3.6 times. This is a significant shortfall. It shows the wall did not merely fail because it was hit by wind. Rather, it failed because it lacked the structural capacity needed to resist the wind loads it was required to withstand.
Evidence from S shows pre-existing cracking and prior movement of the wall which supports a gradual process of deterioration or weakening caused by the wall’s inadequate design or construction. This is consistent with S’s view that long-term cyclic wind loading acted on a wall that was already structurally deficient. The final collapse occurred during the claimed weather event, but the damage flowed from the pre-existing inability of the wall to resist lateral loading and overturning.
I acknowledge the complainant has provided certification from consulting engineers ‘G’ dated 27 May 2026. This confirms G carried out structural inspections during the construction of the project. Further, those inspections found the inspected work conformed with the intent of the design as conveyed by the structural engineering drawing approved by Council.
However, there is absence of any direct evidence or supporting information that:
· shows that all areas, including the said external roof wall, were inspected by G as part of its inspections over the life of the project
· establishes what the ‘accepted engineering practice and principles’ referred to are and if they were consistent with the relevant AS in place at the time of construction
· establishes what information practices, principles and building standards the council relied on at the time of approving structural drawings for the project
· establishes what the ‘intent of the design’ put forward by the structural engineers providing the drawings was given, noting it is referenced in G’s certification as something that needed to be conformed with.
I am satisfied the building standards referred to and relied on by S in providing its reports are the relevant standards for the time of the wall’s construction. I am satisfied the proximate cause of the wall collapse was the inherent inadequacy of the wall’s design or construction which did not meet the relevant standards and recommendations. The storm on 1 July 2025 may have triggered and/or contributed to the failure, but it was not the effective or dominant cause of the damage to the wall.
The expert evidence supports the conclusion that the wall did not meet the relevant design requirements in its unreinforced and unstabilised condition. Given this, I am satisfied it is fair and reasonable to accept the damage was caused by a pre-existing design or construction defect, rather than by the storm event. Further, the policy excludes from cover loss or damage that is caused by defective design or construction.
Insurer’s interpretation of the policy wording is fair
I have carefully considered the complainant’s concerns regarding the insurer’s interpretation and reliance on the policy’s exclusion wording to decline the claim. However, I do not agree with the complainant’s position.
This is because, I am satisfied the policy wording informs:
· the policy excludes from cover loss or damage caused by or arising directly or indirectly from:
> a defect, error or oversight in design, plan or specifications or failure of design
> defective or faulty materials or faulty workmanship
· there exist exceptions to these excluded circumstances where the policy commits to cover resultant loss, destruction or damage where the complainant was not aware of or could not reasonably have been aware of the defective and/ or failure of the wall’s design.
I accept the insurer’s position that the above noted exception does not extend cover to the defective item, which in this case is the wall itself. However, it commits to extend cover to ‘resultant damage’ from the wall collapsing. This would include any resultant damage to other parts of the insured building and/or damage to third party property.
Therefore, I am not persuaded it would be fair to prevent the insurer from relying on the policy exclusions to reduce its liability in these circumstances.
Insurer is entitled to decline the claim
I am satisfied the insurer has shown, on balance, the proximate cause for the damage to the wall is defective design and construction, which is excluded under the policy. The insurer is entitled to decline the claim.
If, however, the complainant has evidence of any resultant damage from the wall collapsing or receiving third party demands for such damage, this is to be provided to the insurer for consideration.
2.3 Why is the outcome fair?
The outcome is fair as it is based on the exchanged information and the policy. The exchanged information shows it is more likely than not that the wall collapsed due to factors excluded under the policy. It would be unfair to require the insurer to accept liability for the damage where it is otherwise not required to under the policy.
3 Supporting information
3.1 The AFCA process
AFCA’s approach is based on fairness
AFCA has determined this complaint based on what is fair in all the circumstances, having regard to:
· the legal principles
· applicable industry codes or guidance
· good industry practice
· previous decisions of AFCA or its predecessor schemes (which are not binding).
The respective parties have completed a full exchange of the relevant information, and each party has had the opportunity to address any issues raised. We have reviewed and considered all of the information the parties have provided.
While the parties have raised a number of issues in their submissions, we have restricted this determination to the issues that are relevant to the outcome.
We assess complaints on available information and circumstances
AFCA is not a court of law. We do not have the power to take or test evidence on oath, or to require third parties to give evidence.
When we assess complaints, we consider:
· available documents
· the recollections of the parties
· all relevant circumstances.
We give more weight to documents created at the time the events occurred. If there are no relevant documents, we will decide what most likely occurred based on the available information.
If there are conflicting recollections and these are evenly weighted, we may find that a claim cannot be established.
3.2 Relevant policy wording
Section 1
Property: Physical Loss, Destruction or Damage
1. Cover
This Section covers:
Physical loss or destruction of or damage to Insured Property caused by an Event occurring during the Period of Insurance and not otherwise excluded.
Unless stated otherwise in this Section 1, the most We will pay per Event is the Sum Insured.
…
2. Definitions Applying to this Section
2.3 Event
An occurrence or accident causing or resulting in sudden and unforeseen, physical loss or destruction of or damage to Insured Property…
…
3. Exclusions Applying to this Section
The following exclusions apply to Section 1 in addition to the General Exclusions.
3.2 We will not cover physical loss, destruction or damage caused by or arising directly or indirectly from:
q) i) defect, error or oversight in design, plan or specification or failure of design; or
ii) defective or faulty materials or faulty workmanship,
but We will pay for resultant loss, destruction or damage to Insured Property resulting from any Event not otherwise excluded by this Section 1, provided that You were not aware of, or could not reasonably have been expected to be aware of, exclusion q) i) or ii);