Home / Youi / Determination 12-25-284504
Determination 12-25-284504
Declined storm damage claim for warped floorboards on the basis of rising damp or seepage exclusion
Summary
The complainant claimed for storm damage to floorboards, which the insurer declined as rising damp or seepage. AFCA found the April 2024 storm was the dominant cause and required the insurer to accept and settle the claim.
The complainant established on the balance of probabilities that storm water overflow was the proximate cause, and the insurer did not prove the rising damp or seepage exclusion applied.
Issues
- Claim denial primary · upheld“The insurer has not proven any exclusions apply; stormwater overflow from the April 2024 storm was the dominant cause of the floorboard damage.”
- Product terms interpretation secondary · upheld“Water pooling and entering the property is stormwater overflow from the area immediately around the premises, not seepage of water from the ground in the sense required by the exclusion.”
Subjects and remedies
home or building damagenatural disasterpay claim
Related
Text of the determination
Determination
|
Case number
|
12-25-284504
|
Financial firm
|
Youi Pty Ltd
Case number: 12-25-284504 26 August 2026
1 Determination overview
1.1 Complaint
The complainant has a home building and contents insurance policy with the financial firm (insurer).
On 28 January 2025, the complainant made a claim for storm damage after discovering warping and blistering in the wooden flooring on the ground level of the building. He says the damage was caused by a storm in April 2024, but he was unaware of the water ingress until the flooring started warping.
The insurer declined the claim on the basis the damage is unrelated to the storm event. Instead, it says the damage was caused by rising damp or seepage which is excluded from cover under the policy.
1.2 Issues and key findings
Is the insurer entitled to decline the claim?
No. The exchanged information shows that stormwater overflow from the April 2024 storm was the dominant cause of the floorboard damage. The complainant has therefore established a valid claim under the policy. The insurer has not proven any exclusions apply.
Why is the outcome fair?
The outcome is fair because the complainant has established a valid claim and the insurer has not proven any exclusions apply. On that basis, the insurer should pay the claim
1.3 Determination
This determination is in favour of the complainant.
Within 14 days of being notified of the complainant’s acceptance of this determination, the insurer is required to accept the claim and settle it in accordance with the policy.
2 Reasons for determination
2.1 Is the insurer entitled to decline the claim?
No. The exchanged information shows that stormwater overflow from the April 2024 storm was the dominant cause of the floorboard damage. The complainant has therefore established a valid claim under the policy. The insurer has not proven any exclusions apply.
The property suffered damage
The insured property is a two-storey sandstone house, built on a concrete slab, and constructed in 2011. The complainant says that between 4 April 2024 until 7 April 2024 there was unusually heavy rain in the vicinity of his property. He says that even though the drainage pits were all working at the time, the amount of water exceeded the capacity of the drains and resulted in the courtyard flooding.
The complainant says the main water ingress was under the front door. He says that he noticed a wet patch on his carpet, but he was not aware of any other damage at the time. As a result, he says he did not make an insurance claim.
In January 2025, the complainant says he became aware of issues with his floorboards. He says that they were warped and some were beginning to rot.
The complainant believes that the water ingress from the April storm event has resulted in the expansion, cupping and buckling of the floorboards in several areas of the house. The areas damaged include:
· the lower entry area
· the two rooms on either side of the entry to the house
· living/lounge room
· hallway
· kitchen.
The complainant has the onus to establish a valid claim
It is established insurance law that the complainant first has the onus to establish the claimed loss is a result of an event covered under the policy. This must be established on the balance of probabilities, meaning that it is more likely than not.
If the complainant is able to establish that the cause of the damage to the floorboards was the storm, then the onus shifts to the insurer to show, on the balance of probabilities, it is entitled to rely on an exclusion under the policy or is otherwise entitled to decline the claim.
Policy cover is subject to terms, conditions and exclusions
The terms and conditions of the policy are set out in the policy documents, including the Product Disclosure Statement (PDS) and the Policy Schedule. The policy is an ‘insured events’ policy. This does mean all loss or damage is covered, only loss or damage covered by one of the insured events.
In relation to storms, the policy covers:
Loss or damage to the insured property caused by storm, lightning, wind, hail, snow and storm water overflow from roof gutters and their downpipes or from the area immediately around the premises.
Where storm is defined as:
a violent atmospheric event which includes a thunderstorm, cyclone or strong wind with or without rain, hail or snow, but not rain showers alone.
The policy specifically excludes loss or damage caused by ‘rising damp or seepage of water from the ground’.
There was a storm event
The complainant says his house was impacted by unusually heavy rainfall that occurred from 4 April 2024 to 7 April 2024.
The complainant has provided an extract from the local newsletter dated 8 April 2024 that says:
SES units received almost 600 requests for assistance between Thursday, April 4, and Sunday evening April 7, as severe storms caused damage and flooding around the region.
He has also provided a severe weather warning issued by the Bureau of Meteorology (BoM) on 5 April 2024 that includes a map of affected areas. This map covers the area where the house is located. The BoM warns of ‘heavy, locally intense rainfall and damaging winds’.
The insurer says that the complainant has not established when the storm event occurred. It says that when the complainant initially lodged the claim, the storm event was said to have occurred on 16 February 2024. However, having reviewed the exchanged information, it is not clear where this date has come from.
When submitting the claim, the complainant said the damage occurred as a result of:
one of the really big floods early last year.
The insurer’s assessor, AB, following its assessment on 8 February 2025, reports that the damage occurred in mid-2024.
Whereas the report by the insurer’s engineer, SC, dated 14 April 2025, says:
based on the provided claim details, we understand that water entered the dwelling (believed to have seeped through proximate to the front door) during a storm event on 16 February 2024.
Having reviewed the exchanged information, there is no mention in the claims file of the storm occurring on 16 February 2024. I am therefore satisfied that the storm event occurred during the period from 4 April 2024 to 7 April 2024 as put forward by the complainant.
I am also satisfied that the extreme weather event during this period involved both intense rain and damaging winds and meets the definition of a ‘storm’ under the policy.
The complainant says the floorboards were damaged by the storm
The complainant says that after the water ingress to his property in April 2024, the moisture damaged his floorboards. This happened over a period of time and did not become noticeable until January 2025 when he lodged his insurance claim.
The complainant relies on the report of his builder, BW, dated 20 March 2026. BW says the damage to the flooring is consistent with this event. He says once water ingress has occurred, the water will be trapped between the concrete slab, the plastic sheeting and the timber flooring. This moisture will cause swelling, cupping and the splitting of the timber. If the affected timber flooring is not removed and dried out, it will continue to expand and spread the damage to other areas of the house.
The complainant also relies on the report from his structural engineer, BD, dated 15 February 2026. BD says:
There is strong evidence of stormwater seepage under the floorboard. This is caused by the rising water level from the stormwater in the courtyard during severe storms such as 1 in 100 year events. During these events the existing pipes struggle to discharge the volume of water accumulating during the storm.
BD says that as the water rises, it can enter the building through any perforations and air vents. There can also be gaps between mortar joints that will allow the water to slowly pass through to the other side of the building and affect the inner floorboards. He says the water marks on the wall indicate that the stormwater may sit in the courtyard for an extended period before draining.
BD says the stormwater load may come from several areas, including:
· the courtyard surface
· roof downpipes
· retaining wall sub-drainage
· surface water from higher ground, including the neighbouring properties.
Further, BD says:
During the inspection, it was noted that area in discussion was damp and there was a distinct water mark on the sandstone wall along the edges of the building.
The insurer says the floorboards were damaged by rising damp or seepage of water from the ground
The insurer disagrees that the damage was caused by a storm. It says the damage to the floorboards has been caused by rising damp or ongoing water seepage and that this is excluded from cover under the policy.
The insurer says that the damp-proof course is not compliant and this has allowed water to rise up the wall and migrate through the slab.
It relies on the report of its assessor, AB. AB says the timber rot near the front door is not typical of a single flood event and is generally caused by constant exposure to moisture. However, he then says that the floor peaking:
could possibly be due to an installation defect, or the site is allowing water to wick into the flooring in these locations. The peaking could also be consistent with a flooding event however no other damages were observed typical of a flood event, ie damaged skirting, plaster or cabinetry.
The insurer also relies on a report from its engineer, SC. SC says the pattern of damage is consistent with long-term water entry and water moving through the slab. He says this is likely due to an inadequate damp-proof course, as there is not enough clearance between the building and the external pavement.
In particular, SC says:
· the moisture readings show there is a constant source of water entering the property
· the expansion joint in the kitchen was completely compressed. He says this indicates long-term water entry. If the damage was caused by a single event, he would have expected the joint to expand again as the flooring dried and contracted
· the cracking and rotting of the floorboards is typical of damage caused by years of ongoing water exposure, rather than a one-off event.
There is conflicting information about the damp-proof course
The complainant says that the damp-proof course at his property is compliant. He says that there is no evidence of rising moisture at the property and it cannot be attributed to non-compliant damp-proof cause as claimed by the insurer.
The complainant’s builder, BW, says that the property is compliant. He says:
· damp-proof course cavity flashing is installed between the base layers of limestone around the perimeter of the walls of the building
· there is a compliant step down to the outer slab to allow for the correct installation of the cavity flashing and damp-proof course
· stormwater management is controlled by concrete surfaces that fall away from the building towards all the stormwater pits and drains
· there is sufficient stormwater management to the perimeter of the building.
The insurer disagrees. Its engineer, SC, says the building code that applied at the time of construction required damp-proof course to be installed 150 mm above the pavement. He says the 150 mm requirement applies as there is no significant slope of the pavement away from the dwelling. He says that the damp-proof course was consistently at a height less than 150 mm and in some places, it was at ground level. SC has provided photographs to support his opinion.
There is conflicting information on whether moisture is entering the walls
The insurer says moisture readings provided by SC on 8 April 2025 show there is a constant source of water entering the property through the base of the walls. SC says elevated moisture levels were detected in the areas of the flooring that were adjacent to the external walls. The highest moisture readings were in the base of the walls, with the level of moisture decreasing with height.
The complainant disagrees with the insurer’s findings. He says that when his builder, BW, inspected his house on 20 March 2026, there was no evidence of rising damp in any part of the lower inner skin of the limestone wall. There was also no evidence of mould on the internal walls. The inspection of the outside also revealed no evidence of rising damp from the outer skin limestone.
BW says moisture readings taken from several areas on this day were all low and within an acceptable range even though it was raining. Further, moisture readings were taken from a damaged area of the floor, and it was shown to be dry.
The April 2024 storm was the dominant cause of the damage
I am satisfied, on balance, that the April 2024 storm was the dominant cause of the floorboard damage.
When an insurance policy uses the term ‘caused by’, this typically means proximate cause.
Proximate cause is a question of fact depending on the circumstances. The proximate cause is not necessarily the first or last or the sole cause of the loss. It is the effective, dominant or operative cause of the loss.
When multiple factors contribute to the same loss, AFCA will consider whether one factor was the ‘proximate cause’. The proximate cause is the real, dominant, or effective cause. It is not necessarily the cause that most immediately preceded the loss. Courts have said that if a first factor would have caused loss in any case, and a second factor would not have caused loss in the absence of the first factor, the first factor is the proximate cause of the loss.
The complainant has provided a plausible explanation for how water from the April 2024 storm entered the property and later damaged the floorboards. His builder, BW, explained how water trapped between the concrete slab, plastic sheeting and timber flooring could cause swelling, cupping and splitting over time. He said if the timber is not dried out, the damage would spread to other areas of the house, in a similar fashion to the pattern of damage observed in this matter.
The complainant’s engineer, BD, also explained how stormwater could rise in the courtyard during a severe storm and enter the property through air vents, perforations or gaps in mortar joints. He provided a detailed explanation of the water run-off in the area and how, during a 1 in 100-year storm event, the drainage would not be able to cope with the volume of water. This could lead to pooling in the courtyard. BD also referred to a watermark on the exterior wall as evidence that storm water had pooled against the building.
I accept the insurer has provided information that supports an alternative explanation. It’s engineer, SC, recorded elevated moisture levels near the external walls, with the highest readings at the base of the walls. SC said this indicated a constant source of water entering the property. SC also said the cracking and rotting of the floorboards is typical of damage caused by years of ongoing water exposure, rather than a single event.
Additionally, SC said the damp-proof course was too close to ground level in some areas and was not compliant. I accept this provides a possible pathway for ongoing moisture entry. However, it does not establish that the damp-proof course was ineffective or that ongoing moisture entry was the dominant cause of the damage.
The complainant’s builder, BW, reached a different view. He said that the damp-proof course was compliant and there was no evidence of moisture in the house when he attended. He recorded low moisture readings, even though it was raining at the time of inspection.
I accept there may have been more than one contributing cause, and it is possible the property may experience some moisture ingress through the walls or slab from time to time. However, the expert information exchanged about moisture ingress and the adequacy of the damp-proof membrane is conflicting.
Other matters also weigh against ongoing moisture ingress being the dominant cause of the damage. BW says the external concrete surfaces fall away from the building and towards the stormwater pits and drains. There was also no visible damp on the lower interior walls. Further, there is plastic sheeting between the concrete slab and the blackbutt timber floor, which would provide some protection from moisture vapour rising through the slab.
For these reasons, I am satisfied the information shows stormwater overflow from the April 2024 storm as the dominant cause of the floorboard damage. Stormwater overflow from the area immediately around the premises is covered under the policy. The complainant has therefore established a valid claim.
Within 14 days of being notified of the complainant’s acceptance of this determination, the insurer is required to accept the claim and settle it in accordance with the policy.
The rising damp or seepage of water from the ground exclusion does not apply
The insurer says the ‘rising damp or seepage of water from the ground’ exclusion applies. It relies on BD’s reference to:
seepage beneath the flooring due to the inadequate drainage and increased hydraulic load, noting water levels rise in the courtyard during storm events.
For the reasons mentioned above, I am satisfied that the stormwater overflow was the dominant cause of the floorboard damage.
The policy covers storm damage, including ‘storm water overflow from roof gutters and their downpipes or from the area immediately around the premises’.
BD’s report said that, during a severe storm such as a 1 in 100-year event, water may collect from several sources, including the courtyard surface, roof downpipes, retaining wall sub-drainage and surface water from higher ground, including neighbouring properties. BD says this water can pool in the courtyard and cause the water level to rise because ‘the existing pipes struggle to discharge the volume of water accumulating’.
I am satisfied the water pooling and entering the property, as described by BD, is stormwater overflow from the area immediately around the premises. It is not seepage of water from the ground in the sense required by the exclusion. BD’s report describes stormwater building up because the drainage system could not cope during an exceptional storm event. It does not show the damage was caused by ordinary groundwater seepage, rising damp, or inadequate drainage in normal weather conditions.
2.2 Why is the outcome fair?
The outcome is fair as the complainant has shown the April 2024 storm was the dominant cause of the floorboard damage. I accept there maybe moisture ingress impacting the property from time to time. However, the information more strongly supports the storm as the dominant cause of the damage. In these circumstances, the insurer should pay the claim.
3 Supporting information
3.1 The AFCA process
AFCA’s approach is based on fairness
AFCA has determined this complaint based on what is fair in all the circumstances, having regard to:
· the legal principles
· applicable industry codes or guidance
· good industry practice
· previous decisions of AFCA or its predecessor schemes (which are not binding).
The respective parties have completed a full exchange of the relevant information, and each party has had the opportunity to address any issues raised. We have reviewed and considered all of the information the parties have provided.
While the parties have raised a number of issues in their submissions, we have restricted this determination to the issues that are relevant to the outcome.
We assess complaints on available information and circumstances
AFCA is not a court of law. We do not have the power to take or test evidence on oath, or to require third parties to give evidence.
When we assess complaints, we consider:
· available documents
· the recollections of the parties
· all relevant circumstances.
We give more weight to documents created at the time the events occurred. If there are no relevant documents, we will decide what most likely occurred based on the available information.