Partial decline of storm claim for house damage and mould after Cyclone Alfred; cash settlement offered for garage damage only
Text of the determination
Determination
|
Case number
|
12-25-271284
|
Financial firm
|
Hollard Insurance Partners Limited
Case number: 12-25-271284 30 June 2026
1 Determination overview
1.1 Complaint
The complainant holds a home and contents policy with the financial firm (the insurer). On 10 March 2025, he lodged a claim for damage to his property on 9 March 2025 following Cyclone Alfred.
The insurer has partially accepted the claim in relation to the damage to the garage. It has declined the claim for the house. It says the moisture ingress resulting in mould at the property has been caused by construction defects, faulty workmanship and non-compliant roofing. Damage caused by these factors is excluded under the policy.
The complainant disputes this and wants the insurer to accept his claim in its entirety.
1.2 Issues and key findings
Is the insurer’s offer of settlement fair and reasonable?
Yes. The exchanged information does not show the storm event, or any other event the policy covers, caused the damage claimed, except for the garage.
Is the complainant entitled to non-financial loss compensation?
No. I am satisfied that the insurer has appropriately handled the claim.
Why is the outcome fair?
The exchanged information shows that, except for the garage, the claimed damage was not caused by anything the policy provides cover for. Therefore, it is fair for the insurer to deny the claimed damage to the remainder of the property. The insurer’s offer of settlement is fair and reasonable for the garage damage.
1.3 Determination
This determination is in favour of the insurer.
Should the complainant accept the determination, within 14 days of receiving written notice of his acceptance, the insurer is to pay the complainant $10,970.61 which includes a 25% contingency uplift.
2 Reasons for determination
2.1 Is the insurer’s offer fair and reasonable?
Yes. The exchanged information does not show the storm event, or any other event the policy covers, caused the damage claimed, except for the garage.
Onus on complainant to establish a claimable loss
The complainant is required to show, on the balance of probabilities (that it is more likely than not), that he suffered a claimable loss under the policy. This means that he must show the loss was caused by a risk for which he is insured.
Once the complainant, on balance, establishes a claimable loss, the insurer is liable for the loss unless it shows an exclusion or limiting condition applies. The insurer has the onus of proving, on balance, the application of the exclusion or condition.
The terms of the policy include the Certificate of Insurance (COI) and the Product Disclosure Statement (PDS). There is no dispute the insurer sent these documents to the complainant.
The policy covers damage caused by one of the listed events. It does not provide cover for all damage. Amongst these events is cover for ‘Storm’. Coverage remains subject to the terms, exclusions and conditions of the policy.
The parties do not dispute that there was a storm (Cyclone Alfred) on 9 March 2025 which caused damage. The insurer has accepted that the storm resulted in damage to the internal ceilings in the garage. It has offered to cash settle the complainant for this damage in the amount of $10,970.61 which includes a 25% contingency uplift.
However, the parties disagree on whether the storm has caused water ingress to the house. The complainant says that because of the storm, the property is now contaminated with mould and is uninhabitable. The insurer disputes that.
Complainant says all damage resulted from Cyclone Alfred
The complainant says that his property was extensively damaged with water ingress following Cyclone Alfred. He says that there is moisture damage to the following:
· garage
· living/dining/kitchen
· laundry
· pantry
· office
· entertainment room
· master bedroom
· bedroom three.
The complainant has provided a residential building inspection report conducted on 6 August 2025 and a standard property inspection report dated 8 August 2025. Additionally, the complainant has provided a post construction report for the property dated 17 April 2024.
The complainant says that these reports show that the property was not damaged prior to Cyclone Alfred and confirm that the property does not have any construction defects as suggested by the insurer.
The complainant has obtained a report from roofer DB dated 23 June 2025. DB says:
· the roof is approximately one and a half years old
· it complies with the applicable standards and is watertight
· there was no ingress apart from over the garage
· the ingress of water into the garage was due to the extreme volume of rain combined with strong winds and water from upper roof downpipe spreader
· the trim dek roof over the garage has leaf guard mesh installed on it, which is not recommended on lower pitch roofs as debris can dam up behind the mesh and cause water to overrun laps in roof sheets
· a downpipe spreader from the roof above should be extended to the gutter below to prevent spills out onto the lower roof over the garage.
The complainant also obtained a report from BM, a mould restorer. The report is dated 15 May 2025. BM notes that the complainant suffers from a medical condition in response to mould. BM says it was engaged to provide a mould and moisture inspection of the property following a:
top down water ingress event during tropical Cyclone Alfred affecting the garage.
BM noted that the complainant was concerned that there were other areas affected by water ingress during the event which could not be visually identified.
BM says:
· a microbiological assessment found high levels of Aspergillus/Penicillium-like spores and fungal hyphae which indicate a microbial contamination issue that warrants immediate and thorough investigation
· fungal hyphae are indicative of recent active mould growth
· water damage and mould growth consistent with a water ingress event were identified in the reported affected areas of the property
· mould growth is expected to be on building materials within interstitial spaces, but further invasive assessment to determine the extent of damage/mould growth will be required.
The complainant has obtained quotes to remediate and repair the property. He has provided a mould remediation quote from BM dated 10 June 2025 in the amount of $98,691.12.
He has also provided a quote for repairs to the property from builder FC dated 13 June 2025 in the amount of $285,238. The quote includes extensive repairs to the property including replacing kitchen and laundry cabinetry and fittings.
The complainant has obtained a report and quote from MP, a mould cleaner, dated 23 June 2025. The quote is in the amount of $311,135.
The complainant seeks payment from the insurer for remediation and repairs to the property based on these quotes.
Insurer obtained expert reports
Following the lodgement of the claim, the insurer appointed builder QA to undertake make safe repairs. QA attended the site to make safe the ceiling and inspect the roof leak. QA found the top window was not sealed and could be the problem with the windy rain from the cyclone. QA removed the wet insulation from the ceiling and all wet plaster and sheeted in ply.
The insurer appointed restorer LR, who provided a report following its attendance on 8 April 2025. LR notes that the complainant reported that no water ingress had occurred to other areas of the property, only the garage. LR also notes that the complainant had engaged a hygienist to conduct sampling and reported that it was found that the property required a full decontamination. However, the results from the hygienist were not provided to LR.
LR noted that at inspection, there was no other visible damage throughout the remainder of the property. There were no signs of elevated humidity, unusual odours, visible mould growth, or water staining in any other areas. LR conducted moisture testing and found no elevated moisture levels.
LR recommended engaging a suitably qualified hygienist to conduct a further assessment and sampling to determine whether decontamination was required.
The insurer appointed QA to conduct a roof assessment. QA attended on 24 April 2025. QA found:
· the roof area above the garage had roofing screws that were over driven, allowing water to enter
· several screws had no rubber washers, and some had washers which were squashed and not working effectively. This was consistent with water ingress
· a 5mm gap between the window and the window trim in the garage was observed, which can cause any directional rain to enter through the gap, although that not thought to be the cause of damage.
QA concluded that the damage to the garage can be attributed to non-compliant building defects. QA says that if the building had been compliant, the resulting damage would not have occurred.
The insurer appointed hygienist RI, to attend the site and provide a mould assessment report. RI attended the property on 12 August 2025 and provided a report dated 3 September 2025. RI inspected the property and conducted mould sampling of both air and surfaces. RI found in relation to the air sample results that:
· the indoor mould ecology in the air samples was consistent with that of the outdoor environment
· the predominant genera detected indoors (Aspergillus/Penicillium and Basidiospores) were also present in the outdoor reference samples but in higher concentrations outdoors
· no abnormal or elevated levels of water damaged indicator moulds were reported
· the indoor airborne mould ecology is deemed to be normal and reflective of outdoor mould conditions and does not indicate any significant mould amplification within the indoor environment.
In relation to the surface sample results, RI found:
· all but one of the surfaces sampled indicated normal and acceptable indoor mould ecology with the exception of the bedroom four’s robe shelf which had an abnormal ecology compared to all other surfaces sampled
· there may have been a water damaged or mould affected content item stored in that wardrobe.
RI recorded that there were no malodours detected which are typically associated with dampness and microbial activity when it conducted its site assessment.
RI noted the evidence of historical top-down water entry into the garage’s southern elevation wall cavity. This was evidenced by an oxidised water run mark on the rear side of the silver wall wrap. RI says that above the location of the water marks is a window with evidence of improper installation of the rubber weather seal. Additionally, RI says the brickwork weepholes located below the window were obstructed with mortar. RI noted that the blockage of the weepholes increases the likelihood that any water entering the façade system may be diverted into the wall cavity or along unintended pathways, contrary to the system’s intended drainage design.
RI observed that directly above the affected area in the garage was a depression in the roof sheeting where water pooled, likely caused by foot traffic. This pooling was noted to occur beneath the point of the upper roof downpipe spreader, compounding the potential for water ingress. RI says that there are likely to be other sections of the silver wall wrap impacted where water can undergo a capillary action, and/or issues with non-compliant roofing and/or poor workmanship.
RI says:
· the issues identified with the window installation and weather seals were observed with other windows inspected at ground level
· the issue with obstructed weepholes was consistently observed throughout the property at ground level
· given the evidence of water ingress into the wall cavity in the garage and dining area, it is likely that other areas are also experiencing some degree of water ingress
· this is likely to be associated with poor workmanship and/or non-compliance issues with the roof covering installation, as well as the window installation and brickwork façade
· micro-condensation events within the property are likely as there is no insulation in the external cavity wall and the framing materials are steel
· this risk of condensation is supported by the documented 332 mornings of condensation events over the last 12 months
· moisture in the outdoor environment, combined with potential issues such as poor workmanship or non-compliant installation of building materials, can affect the wall cavity environment
· this is further influenced by thermal transfer from the indoor or outdoor environment through the plasterboard linings
· these factors together can create a localised microclimate that promotes condensation on the steel framing throughout the year which can encourage mould growth, particularly on materials like the raw paper backing of the plasterboard.
The insurer had its internal assessor (IA) attend the property, together with RI and a building consultant MB, on 12 August 2025 following receipt of the complainant’s quotes. IA notes the history provided by the complainant that he suffers from Chronic Inflammatory Response Syndrome (to mould). The complainant reported that he had suffered from this after residing in a previous property which had high amounts of mould.
IA obtained a history from the complainant in relation to a previously lodged claim with the insurer on 13 January 2025. The claim was for a mould event identified as occurring on 27 November 2024. IA reports that the complainant says that he had identified a mould issue in a downstairs room, on the other side of the property which relates to the current claim. Remediation works were completed by the complainant in the amount of $4,117.30. IA reports that the cause of mould was not identified or confirmed. However, the complainant had not reported any health issues from this area since the remediation works had been completed.
MB provided a report dated 29 August 2025. MB noted that the two-storey dwelling was approximately 12 months old and presented in a near new condition. MB noted:
· there were no visible signs of any storm created openings or any visible storm related damage to the roof sheeting or external wall which would be allowing water to enter the garage, despite the significant weather event which involved high winds
· the absence of structural damage is consistent with the building performing in accordance with expected standards
· the garage has been damaged by water ingress below the lower skillion roof surface
· the laps of the roof sheeting where the downpipe spreader is located (on the centre of the lower skillion roof) have not been sealed along the roof sheet laps, making the installation non-compliant with AS:3500.3 section 3.4.5
· the ends of the roof sheeting where the downpipe spreader is dispersing water have not been turned down in accordance with the manufacturer's instructions
· several roofing screws have been overtightened, also making the installation non-compliant with the manufacturer’s requirements, although that was not the cause of water ingress to the garage ceiling
· the combination of a low pitched roof, water being dispersed directly onto the creased roof sheets where the side laps have not been sealed, together with the ends of the roof sheeting not being turned down have all contributed to wind driven rain and/or capillary action causing water to run back up the underside of the flat trays of the sheeting
· no signs of moisture ingress were noted within the wall cavity of the southeastern corner of the dining/kitchen area which had been reported as having moisture
· the opposite corner had a large amount of silicone to the stepped flashing and a small off cut of flashing had been siliconed to the internal corner and silicone applied. This is the only area identified as a potential point of water ingress.
Insurer says that insured event has not resulted in internal damage or mould
The insurer has partially accepted the claim for damage to the garage. It says there is no evidence of any further damage, including mould, that has been caused by the insured event. It says the expert reports refer to building defect issues which may be contributing to the ongoing moisture issues.
The insurer refers to page 2 of the PDS which says:
This policy provides cover for a defined list of insurable events. It is not a maintenance policy and does not pay out to rectify building defects of faulty workmanship, to improve bad design, or to resolve issues that have occurred due to insufficient maintenance or general wear and tear.
It refers to page 34 of the PDS under the insured event of ‘Storm’ which provides that there is no cover for damage caused when rain enters the building unless the entry point was created by the storm or as a result of significant force. It says that the report from MB shows that the wind gusts experienced were not beyond the threshold for which the property should have been able to sustain, and had the building not had the building defects present, the wind force was insufficient to drive water into the property.
The insurer relies on the policy’s general exclusions to decline the claim for moisture ingress in the southeastern corner of the dining/kitchen area and mould remediation. Those exclusions preclude cover for:
· defects, structural design faults, faulty workmanship or faulty design
· non-compliance with local government regulations or the requirements of a relevant statutory authority
· condensation, mould, mildew …that has not been caused by an insured event.
The insurer says that as the complainant was an owner/builder it was reasonable for him to have been aware of various issues relating to the build, including non-compliance issues. Further, the complainant had obtained a new construction report from AI dated 17 April 2024 which identified several building defects including gutter, windows, cladding gaps and distortions, open joints, holes, marks, under and over driven nails, window and door architrave gaps. Therefore, these issues were within the complainant’s knowledge.
The insurer says that while the previous mould claim related to a different area of the property, it indicates that moisture and mould has been an ongoing issue since 2024 and is unrelated to an insured event.
The insurer submits that despite the above, there is no evidence of mould that has been identified and there is no presence of abnormal or elevated mould ecology levels requiring remediation based on its expert reports.
Insurer has offered to cash settle the garage damage
The insurer obtained a quote 31 May 2025 from QA for the internal repairs to the garage ceiling in the amount of $8,776.49. The insurer has offered to cash settle the complainant based on this quote, together with a 25% uplift for contingencies, being a total amount of $10,970.61.
No evidence of mould prior to the insured event
The complainant provided further information in relation to his previous mould claim. He says that he had lodged a claim as he was feeling unwell and had associated his health issues with mould. However, he says that after a few weeks, his health improved and he believes that he may have reacted to the new paint smells rather than mould. He confirms that the testing undertaken by the insurer at this time confirmed that no mould was found when tested on 31 January 2025.
The insurer has provided information it obtained in relation to the complainant’s previous claim, including the mould and moisture investigation undertaken by hygienist EL and a building report from AB.
EL confirms:
· there was no visual mould growth
· there were no visible signs of moisture ingress
· moisture testing on the linings within the property did not identify any elevated readings
· no odour was detected.
I am satisfied that there was no evidence that the property was affected by mould prior to the insured event. However, I note the defects referred to by RI and MB which support that the property may be susceptible to moisture ingress due to various building defects.
Insurer is not liable for moisture ingress or mould remediation
I am not satisfied that the complainant has established that the property (except for the garage ceiling) requires mould remediation or repairs because of an insured event. I am persuaded by the mould testing undertaken by RI which found normal indoor airborne mould ecology which was reflective of outdoor mould conditions. RI found that the samples did not indicate any significant mould amplification within the indoor environment. RI has provided a credible explanation for surface testing which found an elevated level in the robe of bedroom four.
Importantly, this testing was undertaken in August 2025. This is some five months after the insured event. I am satisfied that if the property had been affected by the insured event, mould would have been detected in the sampling undertaken by RI. Further, it would be expected that in the absence of treatment, the mould would have gotten worse than when it was tested and reported by the complainant’s mould expect BM in mid March 2025.
The report from BM attaches a certificate of analysis from laboratory EU. While it shows high levels of Aspergillus/Penicillium in the entertainment room, the outdoor sample was not tested for those moulds in comparison. However, the level of Cladosporium was noted to be higher in the outdoor sample when compared to the entertainment room.
The report from BM also attaches results from laboratory HE for air and surface mould testing. Consistent with the findings of RI, it shows the outdoor reference samples have higher concentrations for Aspergillus/Penicillium and Basidiospores than most of the indoor samples. HE notes higher concentrations in the laundry, pantry, entertainment room and bedroom three for Aspergillus/Penicillium. However, BM provides no meaningful explanation of the results from the mould testing, particularly when comparing it to the outdoor samples.
Even if mould is present (which I do not accept), the insurer can rely on its exclusion clause for mould as it has not been shown to result from the insured event, particularly noting the absence of moisture ingress other than into the garage.
Further, the policy provides that there is no cover under the insured event of storm for damage caused when rain enters the building, unless the entry point was created by the storm, or when water enters through an opening that is found to be an existing entry point or as a result of defective design. This is qualified with the exception that if it is verified by qualified opinion, that the water entered with such significant force that it would have entered in the absence of the existing entry point or design defect, the insurer will not apply the limitation.
MB and RI say there are no storm related openings at the complainant’s property. However, MB and RI refer to several building maintenance issues relating to workmanship and/or poor design that may have contributed to moisture ingress. MB confirms that the property was built to withstand the wind speeds experienced in Cyclone Alfred and was performing as expected.
I am satisfied, based on MB’s and RI’s assessments, that rain would not have entered the property but for existing entry points or design defects, as the expert evidence supports a finding that the storm force was insufficient to cause ingress otherwise. Therefore, the complainant has not shown that any moisture damage (except for that which occurred into the garage) is a claimable loss under the insured event of storm.
Given the above findings, it is not necessary to consider whether the insurer can rely on its other exclusion clauses to deny the claim.
Insurer’s offer is fair and reasonable
The complainant’s quotes for the garage repairs are excessive. They include replacement of the roller door control and replacement of the air conditioner. The complainant has not shown that these items were damaged by the insured event.
The policy provides the insurer with a discretion as to whether to repair or cash settle the claim. Such discretion must be exercised fairly, reasonably and consistent with utmost good faith.
Given the noted pre-existing issues with the roof, I am satisfied that it is fair for the insurer to cash settle the claim. I am satisfied that the insurer’s quote represents a fair assessment of the insurer’s liability for the repairs to the garage. The insurer’s offer of $10,970.61 which includes a 25% uplift for contingencies and the loss of a lifetime guarantee on repairs is fair in all the circumstances.
2.2 Is the complainant entitled to non-financial loss compensation?
No. I am satisfied that the insurer has appropriately handled the claim.
AFCA can award compensation for non-financial loss
Under our Rules, AFCA can award up to $6,300 compensation for non-financial loss. This must relate to poor claims handling or other actions of the insurer which cause an unusual degree of stress, delay, or inconvenience.
We expect complainants to be moderately robust, and we will not award compensation for the ordinary degree of inconvenience involved in making a claim.
Compensation is not warranted
I acknowledge that the complainant suffers from a significant health condition and has genuine concerns regarding the presence of mould at the property. I accept that this has caused him stress and inconvenience as he has continued to sleep outside the property because of his concerns about the mould contamination.
However, I am satisfied that the insurer considered the complainant’s vulnerability and took active steps to investigate the claim in a timely way. This included arranging timely make safe repairs and undertaking prompt investigations following receipt of the complainant’s reports and quotes.
I am satisfied that the insurer has not caused undue delays or stress and inconvenience due to its claims handling that warrant non-financial loss compensation.
2.3 Why is the outcome fair?
The exchanged information shows that, except for the garage, the claimed damage was not caused by anything the policy provides cover for. Therefore, it is fair for the insurer to deny the claimed damage to the remainder of the property. The insurer’s offer of settlement is fair and reasonable for the garage damage.
3 Supporting information
3.1 The AFCA process
AFCA’s approach is based on fairness
AFCA has determined this complaint based on what is fair in all the circumstances, having regard to:
· the legal principles
· applicable industry codes or guidance
· good industry practice
· previous decisions of AFCA or its predecessor schemes (which are not binding).
The respective parties have completed a full exchange of the relevant information, and each party has had the opportunity to address any issues raised. I have reviewed and considered all the information the parties have provided.
While the parties have raised several issues in their submissions, I have restricted this determination to the issues that are relevant to the outcome.
We assess complaints on available information and circumstances
AFCA is not a court of law. We do not have the power to take or test evidence on oath, or to require third parties to give evidence.
When we assess complaints, we consider:
· available documents
· the recollections of the parties
· all relevant circumstances.
We give more weight to documents created at the time the events occurred. If there are no relevant documents, we will decide what most likely occurred based on the available information.
If there are conflicting recollections and these are evenly weighted, we may find that a claim cannot be established.