Application of underinsurance clause and refusal to reinstate sprinkler system after water damage claim
Text of the determination
Determination
|
Case number
|
12-25-239643
|
Financial firm
|
Lloyd's Australia Limited
Case number: 12-25-239643 27 January 2026
1 Determination overview
1.1 Complaint
The complainant (a not-for-profit ski club represented by its director) holds a specialty commercial business pack insurance policy covering property damage (policy) with the financial firm (insurer). On 20 June 2024, it lodged a claim for water damage from a burst pipe in the roof cavity the previous day.
The insurer accepted the claim. However, after applying underinsurance, it paid $132,710. The insurer declined to replace the sprinkler after its builder (JL) advised the disconnected system was non‑compliant and required redesign.
The complainant says sprinkler costs should be excluded from the value at risk (VAR) since cover was denied. It seeks $199,203 repair costs plus the $10,000 contents and stock limit.
In addition, it says the sprinkler system was disconnected during restoration, had operated safely for decades and seeks reinstatement. It further cites claim‑handling failures and unfair treatment.
1.2 Issues and key findings
Has underinsurance been correctly applied?
Yes. This is because the building sum insured is less than 80% of the estimated VAR. I am satisfied the underinsurance clause has been applied in accordance with the policy terms.
Is the insurer liable for reinstatement of the sprinkler system?
Yes. The system was disconnected only because of the damage. There is no evidence it needed upgrading beforehand. I am not satisfied the policy required it to be updated to current standards before the claim for cover to apply.
Is the complainant entitled to compensation for non-financial loss (NFL)?
No. On balance, most delays resulted from the dispute over policy entitlement. For a not-for-profit entity, the impacts are financial and operational. I am not satisfied they are compensable NFL.
Why is the outcome fair?
The outcome is fair because the insurer applied underinsurance correctly, must reinstate the sprinkler it disconnected, and addressed delays by waiving the excess (which sufficiently resolves the organisational inconvenience).
1.3 Determination
This determination is substantially in favour of the insurer. Within 14 days of being notified the complainant accepts this determination, the insurer is required to act in accordance with sections 2.1 and 2.2 below.
2 Reasons for determination
2.1 Has underinsurance been correctly applied?
Yes. This is because the building sum insured is less than 80% of the estimated VAR. I am satisfied the underinsurance clause has been applied in accordance with the policy terms.
Policy cover is subject to terms, conditions, and exclusions
The policy covers the period from 19 March 2024 to 19 March 2025. Coverage is defined in the policy wording (PW) and policy schedule (PS), which must be read together. Relevant terms are outlined in section 3.2.
There is no dispute the complainant received a copy of the policy documents. The insurer is entitled to rely on the terms of the policy in assessing the claim.
The policy covers loss or damage to the insured property at the risk address during the period of insurance. Relevantly, cover is subject to an underinsurance clause which says if you insure your building for less than 80% of what it should have been insured for, then any claim payment will be reduced in the same proportion.
In addition, the policy covers additional reinstatement costs needed to meet current laws or council rules after damage, if those requirements did not apply beforehand. Coverage is capped by the remaining policy limit, and under‑insurance does not apply.
The requirement to install and maintain fire‑protection and safety equipment to the relevant Australian Standards (AS) is a risk‑management condition. The policy also includes a condition precedent requiring all extinguishers, hose reels, hydrants, and fire‑detection systems to be regularly serviced and fully compliant with AS for the entire policy period.
Insurer partially accepts claim
Following claim lodgement, the insurer appointed its restorer (RX) to perform restoration works. During restoration, the sprinkler system was disconnected to facilitate the works.
It was identified as non-compliant due to its age. JL advised it could not be reinstalled without a full redesign to meet current standards.
The insurer obtained reinstatement quotes from JL:
· building reinstatement (excluding sprinkler system): $199,203 (excl. GST)
· fire sprinkler reinstatement: $326,640 (excl. GST)
On 24 March 2024, the insurer issued a partial claim declinature for costs associated with replacing and upgrading the sprinkler system to a compliant standard.
Underinsurance applied to the claim
The insurer says the building was insured for $525,000, while the assessed VAR was $1,148,258 (ex‑GST). The adjuster (SA) confirmed the cost of a new compliant sprinkler system was excluded from the VAR.
This is because the system was non‑compliant at the time of loss, so reinstatement must reflect the ‘as was’ condition. Using the $525,000 sum insured, the adjuster assessed adequacy at 67% against a VAR of $985,058 (excluding demolition and compliant sprinkler upgrades):
· adjusted replacement cost: $985,058 (excl. GST)
· 80% VAR threshold: $788.046
· sum insured: $525,000
· adequacy ratio: 67%
As a result, the original repair cost of $199,203 was reduced to $132,710, and this amount, (gross of the waived excess) was paid as a cash settlement without prejudice to the AFCA complaint.
Parties disagree on VAR
The complainant says the insurer’s payout was miscalculated because the cost to upgrade the sprinkler system ($326,640) should not form part of the VAR. This is because the insurer denied cover to reinstate and upgrade the decommissioned system.
It says sprinkler costs inflated the underinsurance adjustment to 67%. Excluding the sprinkler cost, as per SA’s breakdown, reduces the VAR to $658,418 (i.e. $985,058 less $360,640), resulting in about 99.7% adequacy after the 80% tolerance. On this basis, it says it is entitled to full repair costs.
SA confirmed the $326,640 cost to make the non‑compliant sprinkler system compliant is excluded from the VAR. This is because the VAR reflects reinstatement ‘as was,’ not redesign or upgrade costs.
SA provided two VAR estimates, one including the original (non‑compliant) system and one excluding all sprinkler cost, with the relevant VAR determined to be $985,058 based on an estimate including the non-complaint system.
It says underwriting confirmed the sum insured was intended to include the original sprinkler system only, not the upgrade. The insurer says the $326,640 upgrade cost is correctly excluded, and the correct VAR was used in the loss calculation.
Complainant’s VAR approach is misconstrued
I am not persuaded the complainant’s VAR approach is correct. This because it is conflating validating the adequacy of the sum insured at the commencement of the policy with the insurer’s decision the deny the cost of reinstating the sprinkler system.
The VAR represents the estimated cost to fully reinstate the insured property following a hypothetical total loss, in accordance with current construction and regulatory requirements. It is used to assess the adequacy of the sum insured and presence of underinsurance.
Where a sprinkler system would be required in a total rebuild, its costs form part of the reinstatement exposure and must be included in the VAR assessment.
The fact the insurer may dispute or deny the cost of reinstating the system in a partial loss does not alter the VAR, which is a pre-loss risk assessment, not a measure of policy liability in a particular claim.
I consider the insurer’s use of a VAR based on reinstating the property ‘as‑was’ with the legacy sprinkler system is consistent with the policy coverage.
On balance, I accept the insurer’s replacement value calculation because:
· the policy says underinsurance is based on the building’s full value at the start of the insured period, which includes the pre‑existing sprinkler system
· the loss exceeds 10% of the building sum insured and the sum insured is less than 80% of the building’s full value
· the complainant has not provided any persuasive evidence to refute the insurer’s VAR estimate.
VAR and settlement require adjustment
During the AFCA complaint, the insurer reviewed the ‘architects and other consultants’ fees’ additional benefit and confirmed this benefit sits on top of the $525,000 building sum insured.
Therefore, professional fees should not form part of the VAR. It removed $46,907 in professional fees from the VAR.
The resulting loss calculation is:
· revised replacement cost (ex‑GST): $938,150
· Sum Insured: $525,000
· 80% VAR threshold: $750,520
· adequacy ratio: 69.95%
· adjusted repair cost: $199,203 × 69.95% = $139,345
On 19 March 2025, the insurer assessed the underinsured repair cost at $132,710 and offered a cash settlement due to the non‑compliant sprinkler system. Payment was made in January 2026 after the complainant demonstrated urgent financial need. The settlement did not include any uplift for risk transfer or the time elapsed since JL’s June 2024 quote.
I am satisfied it is fair in all the circumstances for the insurer to pay the complainant additional:
· $6,635 (the difference between payment and adjusted repair cost)
· $13,935 (10% contingency uplift on total adjusted repair costs)
Within 14 days of receiving notice the complainant accepts this determination, the insurer is required to pay the complainant:
· $20,570 ($6,635 plus $13.935)
· interest on the total adjusted repair cost ($139,345) calculated in accordance with section 57 of the Insurance Contracts Act (1984) from 19 March 2025 to 14 January 2026.
In addition, the insurer has agreed to pay the full sublimit of $10,000 for the contents and stock claim. Within 14 days of receiving notice the complainant accepts this determination, the insurer is required to pay the complainant $10,000.
2.2 Is the insurer liable for the reinstatement of the sprinkler system?
Yes. The system was disconnected only because of the damage. There is no evidence it needed upgrading beforehand. I am not satisfied the policy required it to be upgraded to current standards before the claim for cover to apply.
Parties disagree on sprinkler system compliance
The parties agree the sprinkler system was not damaged in the insured event. The insurer’s fire services contractor says the system has never been complaint since it was installed 50 – 60 years ago.
The system was disconnected during restoration. JL says it cannot simply be reconnected because it is non‑compliant and would need redesign and full replacement to meet current codes.
The insurer relies on the ‘additional cost of reinstatement’ term in the policy, which excludes costs required to meet compliance if those compliance issues existed before the damage.
It cites an email from SA (9 March 2025) referring to its expert (25 August 2024) and builder (JL), stating the system has multiple non‑compliant features, including:
· a shared water supply with the building
· no separate trace line to prevent freezing
· the absence of key components such as an alarm valve, drain valve, testing facility, monitoring devices, and a block plan.
The complainant disagrees. It says the system was installed in the 1960s and it was unaware of any compliance issues. The system includes a check valve, gate valves, and measures to prevent freezing.
The complainant says the system was regularly maintained and inspected by staff and by the Country Fire Authority (CFA) every six months. It supplied a CFA inspection certificate dated 4 May 2024 showing all fire equipment passed with no compliance issues recorded.
No evidence system was non-complaint
On balance, I am not satisfied the sprinkler system was non-complaint prior to the loss. This is because the assertion the sprinkler system was non-complaint is not supported by evidence of pre-loss illegality or regulatory breach.
The system was installed in the 1960’s. There is no evidence it was unlawfully installed at the time of installation and was accepted as lawful prior to the loss.
I am not satisfied the fact it may not meet current industry and design standards establishes non-compliance for policy purposes. There is no evidence to show the complainant was required to upgrade the system prior to the loss, nor any enforcement action or recertification notice had been issued.
In addition, while the insurer and its experts say the sprinkler system was non‑compliant with any code, it has not identified the specific codes or explained how they were breached. In the absence of this detail, I am not satisfied they have shown the system was non‑compliant.
Insurer cannot rely on policy condition or condition precedent
The insurer says the sprinkler system was non‑compliant with current AS before the loss and therefore it does not have to reinstate or upgrade it. It says compliance with current AS is a risk management condition and condition precedent under the policy.
It maintains even if the system was compliant when installed decades ago, the obligation is ongoing, it must meet current standards and be maintained per AS 1851 during the policy period. Failure to do so breaches the policy and justifies excluding sprinkler upgrade costs.
I am not satisfied these conditions allow the insurer to exclude the sprinkler system reinstatement costs. This is because:
· there is no evidence the system was unlawfully installed under the standards in place at the time
· it was accepted as operational before the loss
· there is no indication of any statutory breach or prior requirement to upgrade.
Properly read, these provisions require lawful installation and ongoing maintenance, not retrospective upgrades of compliant legacy systems. The system was only disconnected due to insurer‑authorised works, and there is no evidence its age or condition contributed to the loss.
Insurer is liable for costs to reinstate the sprinkler system
On balance, I am satisfied the insurer must reinstate the sprinkler system. This is because although the system was not damaged by the event, it became non‑operational only because it was disconnected during insurer‑authorised make‑safe works. This left the complainant in a worse position than before the loss, when the system was functioning.
Any redesign or upgrade requirements arise solely because of that disconnection. To the extent current regulations now require the system to be upgraded, I am satisfied they were triggered by the restoration work and would not have arisen but for the insured event.
The additional‑cost‑of‑reinstatement benefit covers compliance costs created by repair works, not voluntary upgrades of lawful legacy systems. I am satisfied the complainant is seeking restoration of a critical fire‑safety system disabled by the claim works.
Requiring it to fund reinstatement would be unfair, inconsistent with indemnity and the policy’s intended operation.
Within 14 days of receiving notice the complainant accepts this determination, the insurer is required to:
· appoint an independent fire engineer to:
> determine the lawful requirements to reinstate the decommissioned sprinkler system
> identify any mandatory compliance upgrades triggered by this.
· obtain contractor pricing based on these scopes of work including a quantity surveyor review
· cash settle the complainant the:
> reasonable cost of reinstating the damaged sprinkler to its pre loss function as part of the building reinstatement cost, subject to the remaining policy limit and the application of the underinsurance clause, plus a 10% uplift for the transfer of repair risk
> incremental uplift required solely due to statutory or regulatory requirements under the additional cost of reinstatement clause, subject to the remaining policy limit and without application of the underinsurance clause, plus a 10% uplift for the transfer of repair risk.
2.3 Is the complainant entitled to NFL?
No. On balance, delays resulted from the dispute over policy entitlement rather than poor claims handling. For a not-for-profit entity, the impacts are financial and operational. I am not satisfied they are compensable NFL.
AFCA’s approach to NFL
AFCA can award non-financial loss in circumstances where an insurer has made an error or mishandled a claim in a way that causes undue stress and inconvenience to an individual. Generally, AFCA would award this kind of compensation to a natural person, such as an individual or sole trader.
Complainant not entitled to NFL
The complainant says the insurer has not acted in utmost good faith; first by refusing the claim without proper cause due the presence of asbestos in August 2024, and then by unreasonably delaying assessment for seven months after granting indemnity.
While I acknowledge the organisation is a not‑for‑profit and its committee members experienced frustration and inconvenience dealing with the prolonged process, the complainant is an incorporated entity, not an individual.
A company, whether commercial or not‑for‑profit, cannot experience personal stress, anxiety, or emotional harm, which are the main core elements NFL is designed to compensate.
I am satisfied any impact from the insurer’s claims handling relates to operational disruption, inconvenience in coordinating repairs, and the practical and financial difficulty of not being able to use the premises for a period. These effects are business impacts, not personal emotional impacts on an individual.
The insurer acknowledged delays and offered to waive the excess. On balance, I am satisfied this reasonably addresses the inconvenience caused at an organisational level.
The insurer is not required to pay NFL.
2.4 Why is the outcome fair?
The outcome is fair because the insurer applied the policy correctly, must reinstate the sprinkler it disconnected, and addressed delays by waiving the excess (which sufficiently resolves the organisational inconvenience).
3 Supporting information
3.1 The AFCA process
AFCA’s approach is based on fairness
AFCA has determined this complaint based on what is fair in all the circumstances, having regard to:
· the legal principles
· applicable industry codes or guidance
· good industry practice
· previous decisions of AFCA or its predecessor schemes (which are not binding).
The respective parties have completed a full exchange of the relevant information, and each party has had the opportunity to address any issues raised. We have reviewed and considered all of the information the parties have provided.
While the parties have raised a number of issues in their submissions, we have restricted this determination to the issues that are relevant to the outcome.
We assess complaints on available information and circumstances
AFCA is not a court of law. We do not have the power to take or test evidence on oath, or to require third parties to give evidence.
When we assess complaints, we consider:
· available documents
· the recollections of the parties
· all relevant circumstances.
We give more weight to documents created at the time the events occurred. If there are no relevant documents, we will decide what most likely occurred based on the available information.
If there are conflicting recollections and these are evenly weighted, we may find that a claim cannot be established.
3.2 Policy terms
|
Page
|
Description
|
13, 14
|
Claims Conditions
These Claims Conditions apply to all Sections of the Policy. In addition to these Claims Conditions, the General Conditions and/or separate Specific Conditions of each Section also apply.
…
6) Under insurance
The Property Damage and Business Interruption Sections of this Policy are subject to an under insurance/average condition. The effect of this condition is that if, at the time of loss the Sum Insured is less than the full value of the property or income insured, then You may not be covered for Your full loss. It is Your responsibility to ensure the adequacy of Sums Insured and You should re-assess these Sums Insured during the currency of the Policy and prior to renewal each year
…
|
16, 17
|
Risk Management Conditions
These Risk Management Conditions apply to all Sections of the Policy. In addition to these Risk Management Conditions, the General Conditions and/or separate Specific Conditions of each Section also apply.
…
4) Fire Protection & Safety - Equipment and Maintenance Condition
It is a condition of this Policy that You must adhere to the applicable Australian Standards for the installation and maintenance of all required Fire Protection & Safety equipment at the Risk Address. For Your reference, these standards generally include:
a) AS 2441 Installation of fire hose reels
b) AS 1221 Fire Hose Reels Maintenance
c) AS 2444 Portable fire extinguishers and fire blankets - Selection and location
d) AS 1851 Maintenance of Fire Protection Systems and Equipment
e) AS 3786 Smoke alarms
Full details of each Australian Standard can be found at - www.standards.org.au
…
|
21
|
Section 1 – Property Damage
…
Definitions Applicable to this Section
…
Full Value means the amount that would be required as the Total Sum Insured, sufficient to allow Us to fully indemnify You within the terms and conditions of this Section for a total loss of Property Insured at a Risk Address.
…
The Cover
Subject to the terms, exclusions, definitions, endorsements and limitations of this Policy, We will pay You in accordance with the basis of settlement for Loss of or Damage to Property Insured occurring at the Risk Address during the Period of Insurance.
…
|
27
|
Basis of Settlement
Unless otherwise specified in the Schedule and subject to any limitation or restriction applying to any specific additional benefit, special benefit, specific condition attaching to the basis of settlement or specific condition, claims will be settled on the following basis:
…
5) Additional cost of reinstatement:
In the event of Loss or Damage to a Building which is not specifically noted in the Schedule as being insured for Indemnity Value this Section extends to cover those additional costs to reinstate Buildings at the Risk Address (including demolition and dismantling) necessarily incurred to comply with an Act of Parliament or council by-law or regulation that occur as a result of Damage under this Section, provided that compliance with the Act of Parliament or council by-law or regulation was not required to have been complied with prior to the Loss or Damage to the Buildings.
Provided further that We will not pay more than the extent that the Limit of Liability for the Risk Address has not been exhausted.
The Under insurance/average specific condition shall not apply to this basis of settlement clause;
…
|
28, 31
|
Specific Conditions Attaching to the Basis of Settlement
…
12) Under insurance/average
This specific condition applies if the Total Sum Insured at a Risk Address is less than 80% of the Full Value applicable for the Risk Address. In the event of Loss of or Damage to Buildings, Contents, Stock or Other Items which is covered under this Section, We will not be liable for more than that proportion of the Loss or Damage that the Total Sum Insured at the Risk Address bears to 80% of the Full Value at the Risk Address at the time of the start date of the Period of Insurance.
Provided that:
a) We will not pay more than the Limit of Liability for the Risk Address; and
b) this specific condition will not apply if the amount of any Loss or Damage does not exceed 10% of the Limit of Liability applicable for that Risk Address.
Example:
Full Value $520,000
80% of Full Value $416,000
Total Sum Insured $200,000
Therefore if a $140,000 loss occurs, We would pay: ($200,000/$416,000) x $140,000 = $67,308.