Quality of replacement timber flooring installed after water damage claim; complainant sought removal and replacement
Text of the determination
Determination
|
Case number
|
12-25-233505
|
Financial firm
|
Allianz Australia General Insurance Limited
Case number: 12-25-233505 13 April 2026
1 Determination overview
1.1 Complaint
The complainant holds a home building and contents insurance policy (policy) with the financial firm (insurer). On 29 July 2024, a claim was lodged for water damage caused to the insured property after an escape of liquid event from the washing machine.
The insurer has accepted the claim. The complainant is dissatisfied with the new timber flooring (flooring) installed by the insurer. He believes, given the issues identified with the floor installation, the insurer should cover the cost to remove and replace the flooring.
The insurer accepts there are some minor issues that require rectification, which it has offered to rectify. However, it says the expectation to remove and replace the flooring is not reasonable in the circumstances.
1.2 Issues and key findings
Has the insurer fulfilled its obligations under the policy?
No. The exchanged information shows it most likely the insurer has not met its policy obligations with respect to repairing the damaged flooring at the insured property.
Is the complainant entitled to non-financial loss compensation (NFL)?
Yes. The insurer is to pay the complainant $2,000 in NFL.
Why is the outcome fair?
The outcome is fair as it is based on the exchanged information and the policy. The exchanged information shows it is most likely that the insurer has not met its obligations under the policy with respect to the quality and level of repairs authorised under the claim. Given this, it is fair that the insurer be required to arrange the necessary rectification works or cover the cost to remove and replace the flooring if required. It is also fair that the insurer pays the complainant NFL for his poor experience over the life of the claim.
1.3 Determination
This determination is in favour of the complainant.
The insurer is to arrange settlement of the claim as set out in section 2.1 of this determination. The insurer is to pay the complainant $2,000 in line with the AFCA Rules.
2 Reasons for determination
2.1 Has the insurer fulfilled its obligations under the policy?
No. The exchanged information shows it most likely the insurer has not met its policy obligations with respect to repairing the damaged flooring at the insured property.
The policy is an insured events contract of insurance
The insurer provided the complainant with the relevant policy documentation including the product disclosure statement (PDS) and certificate of insurance (COI). I accept the insurer is entitled to rely on the policy provisions to assess its liability under the claim.
The policy covers the insured property against loss or damage caused by one or more of the listed insured events, including ‘Water and other liquid damage’. Cover under the policy is subject to the conditions, limitations and exclusions specified in the PDS.
The PDS states if the insurer agrees to cover the complainant’s claim for loss or damage to the insured building:
· it will pay the reasonable cost of repairing or rebuilding the damaged part of the building
· it will pay for the damaged part of the building to be repaired to the same condition as when it was new.
There is no dispute the insured building has been damaged by an event that triggers cover under the policy. The dispute relates to the parties’ positions on the quality of the floor repairs arranged by the insurer.
Complainant is dissatisfied with the flooring installed by the insurer
The insurer appointed consultants ‘AM’ to assess the cause and extent of the damage. AM confirmed significant damage to the flooring and which would require replacement in the areas of damage. The insurer appointed building consultants ‘W’ which in turn sub-contracted ‘R’ to complete the works.
The complainant informed the insurer of his concerns with the installed flooring which include:
· the flooring has been installed out of square and angular to the internal surfaces of the home. He is of the view this gives the perception that the house is out of square
· he notes deep gouging in the timber through various areas
· there are large gaps between the timbers due to poor installation, and which have been filled with putty or glue in the attempt to disguise the failings
· miscuts and notches have unnecessarily been made in the timber with attempts made to disguise them
· sealer has been applied directly on top of dirt and large debris
· there exist extreme degrees of height fluctuation throughout the flooring
· there exist issues with the skirting boards and beading throughout.
Each party relies on their preferred consultants’ assessments and reports
On being informed of the complainant’s dissatisfaction with the quality of repairs, the insurer appointed ‘AT’ to inspect the replaced flooring. I acknowledge AT is described as being the peak body for timber floors and the timber flooring industry throughout Australia and New Zealand. It is a not-for-profit member based association that delivers industry specific services and technical information to its members and the community.
I acknowledge the complainant has raised concerns about AT’s independence and suitability to assess and provide a report on the flooring. However, I am not satisfied there is any persuasive evidence to bring into question AT’s independence, and I accept AT is suitably qualified to complete such assessments.
AT inspected the flooring on 26 March 2025 and has provided a report dated 29 March 2025. I have carefully considered this report and note:
· AT formed the view that the new flooring initially represents very well with the appearance consistent with that of a new installation
· the flooring appeared to taper by around 80mm along the longest length of the flooring. Although this was visible when focusing on the measurement apparatus, AT says the skew was not really visible when focusing on the broader installation
· the flooring appeared to taper by around 50mm along the length of the dividing wall in the areas of the games room and passageway
· one of the ends of the boards adjoining the return threshold board in bedroom two had been cut too short. Multiple other boards had been cut at different angles which would allow the return threshold board to sit squarely across the junction. These were noted to have been filled with a coloured filler
· AT confirms the presence of sanding inconsistencies around several threshold boards that meet different tiled areas
· the threshold board installed adjacent to the entry to the kitchen (near the tiled entry passageway) was noted to have a sanding imperfection to the board structure in the top left-hand corner of the board (approximately 50mm in size). This was noticeable from a standing position. A similar sanding imperfection was also noted in the bathroom threshold board towards the right-hand side (near the doorframe)
· AT confirms that a slight dip had occurred from the sanding process at a perimeter board in the rear passageway measuring approximately 100mm in length with a dip up to 4.04mm and around 40mm in width
· there exist issues with fitting of a few lengths of the perimeter beading which AT confirmed would require rectification.
AT acknowledges that the complainant has a valid point that the new flooring does not run parallel to some of the building structures but that it was not really noticeable. AT considers this a subjective issue and says in such circumstances seeking industry consensus is recommended. AT sought the opinion of three accredited ATFA inspectors.
I note these representatives did not complete assessments of their own and the advice provided is based on information provided to them by AT. The unanimous consensus is said to be that whilst there do appear to be some issues with the flooring installation, requiring complete removal and replacement would be disproportionate to the noted issues. AT recommended remediation works to include:
· the return threshold board that is fitted at the doorway of bedroom two be removed and replaced but with the board ends adjoining this, cut squarely and accurately to improve the fitment of this board
· re-sanding of some threshold boards to remove some sanding inconsistencies to address these concerns, both of which would then allow for these boards to be sanded in isolation with the floor coating applied and built up to the same level as the general flooring
· this then be followed by cutting back the entire floor installation and re-coating the broader installation
· the replacement and correct fitment of the two lengths of beading against the kitchen cabinetry and glazed dining area window.
The complainant, dissatisfied with AT’s report and associated offer of rectification works from the insurer, appointed his flooring expert ‘M’. M completed an assessment and provided a report dated 26 November 2025. With respect to the quality of flooring installation, some of the concerns raised by M include:
· the concrete sub-floor was not adequately prepared prior to installing the flooring
· the presence of significant deviations in floor levels across the entire floor expanse. M notes this to be inconsistent with requirements of the Western Australia Guide to Standards and Tolerances 2019 (Guide) – Section 15.08 Levelness of Timber Floor
· the flooring exhibits a deviation of 85mm across the length of the floor due to R failing to establish a proper datum line prior to installation. This being non-compliant with AT’s standards
· severe edge bonding throughout the installation
· failure to meet standardised sanding protocol and visual quality objectives.
M concludes that given the various issues with the installation of the flooring, the structural and aesthetic integrity of the floor has been compromised beyond repair. It recommends a total reinstallation of the flooring.
Evidence supports presence of various installation quality issues
The insurer relies on the comments from its appointed consultants and says when assessed objectively against recognised industry standards, the flooring installation:
· is structurally sound
· performs as intended
· meets industry tolerances in the majority of respects, and
· does not warrant full replacement.
I am not persuaded this is a fair and reasonable position in these circumstances. I accept when considering each of the issues with the flooring in isolation, they may appear minor. However, when considered collectively, I am satisfied it is fair to conclude that the quality of installation is not to the standard reasonably expected of a professional or meets the requirements of the policy.
I acknowledge the insurer says the complainant relies on the incorrect criteria in classifying the flooring installation as well as the testing methods relied on by the complainant. However, the insurer has not provided any evidence of what the alleged correct criteria or standards would be in this respect.
The insurer, having had the opportunity, has not provided any persuasive information to counter the issues identified by M regarding the levels and/or flatness noted across the flooring. To simply disagree with and refute M’s methods and findings is not adequate or persuasive in the absence of the insurer establishing what standards, guides or industry requirements should be relied on.
I am not satisfied the insurer has adequately addressed the issues identified with the concrete subfloor to which the flooring has been installed. The insurer appears to say the responsibility to ensure the concrete subfloor was adequately level rests with the party that laid it and not W or R.
However, I am satisfied the exchanged information shows evidence of damage to the concrete subfloor which is most likely to have occurred when the original flooring was removed. I am satisfied there is clear evidence of deviations in the level/flatness across the new flooring. I acknowledge it may not be R’s responsibility to ensure the sub-floor was level.
However, I am satisfied it is reasonable to expect a professional and capable repairer to at the very least check if the levels across the concrete subfloor were acceptable or would cause an issue in the installation. Further, that if in its opinion the level of concrete subfloor was going to impact on the flatness/levels of the flooring, that this should have been discussed with the complainant.
This in my opinion also applies to R’s decision to align the flooring with the edge of the ceramic tiles in the kitchen, which in R’s opinion is the first visual reference point for the flooring when entering through the front door. I accept in R’s opinion this was the best course of action, however, as recognised by AT this is a subjective view.
I believe R should have either followed the alignment of the original flooring or discussed its opinion regarding alignment of the flooring with the complainant. This is consistent with expectations and requirements provided in the Guide. The Guide recommends the contractor, before starting the works, should inform the owner of any potential circumstances and concerns that may have a detrimental effect on the standard of the new works.
I am satisfied the exchanged information, including photos, shows it is more likely than not that the pre-installation preparation works were not to an acceptable standard. I find M’s investigation and findings regarding the pre-installation issues and deviations in levels/flatness across the flooring to be more persuasive.
Given the issues identified by AT and later I am not satisfied it has been shown the flooring has been installed to the required quality and standards. This includes significant deviations in the floor levels/flatness exist in many locations across the installed flooring, and which requires rectification. The insurer has not provided persuasive information to the contrary including but not limited to the alleged correct building standards.
I note the insurer’s concerns regarding the metre by metre mapping image included in M’s report, and which I accept was not prepared by M. It appears to have been prepared by the complainant, said to be an engineer himself. I accept M should not have included this in its report and/or should have clarified its source. However, other than expressing a view that this should be disregarded, the insurer has not provided any alternative detailed mapping or measurements to counter M’s findings.
Similarly, the insurer takes issue with M’s method of testing/measuring the deviations in the flooring levels advising M places weight (hand pressure) at one end of the straightedge tool, skewing the results. The insurer has however not provided any compelling alternative evidence of measurement taken to the same detail and level as M.
I am satisfied even if M were to have weighed one end of the testing tool, it is fair to accept the photos and other evidence clearly support the concerns raised regarding deviations across the flooring. I accept it would be unfair to require the complainant to simply accept and live with these issues, especially given there is no assertion or evidence of the original flooring presenting with such issues.
Insurer to ensure repairs are adequate in line with policy obligations
I am not satisfied the overall quality of workmanship and therefore the installation of the flooring meets the required standards or fulfills the insurer’s obligations under the policy.
As noted above, I accept several of the issues identified by the experts when viewed in isolation are minor. However, I am satisfied it is fair to conclude when all of the various issues are considered collectively, it is reasonable to find the works are not to an acceptable quality.
The insurer’s obligation under the policy is to repair/replace the damaged flooring to the standard as when new. I have not been provided with any evidence to show the original flooring presented with any of the noted issues, especially when new.
I accepted it is fair that the insurer first be allowed the opportunity to remedy all the noted issues without the need to completely remove and replace the new flooring. However, if this is not possible and/or if found that it would be more economical to replace the flooring then it is fair that the insurer (at its discretion):
· proceed with arranging the removal and replacement of the flooring, or
· pay the complainant what it will cost to remove and replace the flooring. This is to be based on an actionable scope of works and repair quote from a suitably qualified repairer.
Alternatively, at its discretion, the insurer can choose to proceed directly to a cash settlement based on an actionable scope of works and repair quote from a suitably qualified repairer. The insurer is commence the necessary remediation works or cash settle the claim within 21 days of receiving notice of the complainant’s acceptance of this determination.
In the interest of completeness, the insurer will also (it is needed) cover the complainant for the cost of temporary accommodation equal to the time it will take to complete the works.
Finally, subject to being provided with proof of payment, the insurer is to reimburse the complainant for expenses he may have incurred in obtaining the report from M as well as any other claim related expenses up to a maximum of $3,000. If the complainant has already incurred such expense, the insurer in line with section 57 of the Insurance Contracts Act 1984, is to pay interest from the date the complainant made such payment to the date on which the insurer issues the reimbursement.
2.2 Is the complainant entitled to NFL?
Yes. The insurer is to pay the complainant $2,000 in NFL.
AFCA Rules allow for an award of NFL in certain circumstances
AFCA Rule D 3.3 allows for an award of up to $6,300 for non-financial loss compensation, if the insurer caused the complainant to suffer an unusual degree or extent of inconvenience, delay or interference. AFCA takes a conservative approach when considering any award of compensation.
An award of non-financial loss compensation under the Rules is based on an unusual degree or extent. This would not encompass the normal degree of inconvenience a person would suffer when lodging an insurance claim or in a dispute with their insurer.
Insurer is to pay the complainant $2,000 in NFL
I am satisfied the exchanged information supports the view that the complainant has experienced undue levels of stress, anxiety, inconvenience and delays. This relates to the insurer’s failure to meet its obligations under the policy and the impact this has had on the complainant’s day to day experience over an extended period of time.
Further, that its failure to acknowledge the noted issues with the quality of the works has only further added to the complainant’s poor experience over the life of the claim. Given this, and in line with the AFCA Rules, I am satisfied it is fair that the insurer pays the complainant $2,000 in NFL. This is to be paid within 14 days of receiving notice of the complainant’s acceptance of this determination.
2.3 Why is the outcome fair?
The outcome is fair as it is based on the exchanged information and the policy. The exchanged information shows it is most likely that the insurer has not met its obligations under the policy with respect to the quality and level of repairs authorised under the claim. Given this, it is fair that the insurer be required to arrange the necessary rectification works or cover the cost to remove and replace the flooring if required. It is also fair that the insurer pays the complainant NFL for his poor experience over the life of the claim.
3 Supporting information
3.1 The AFCA process
AFCA’s approach is based on fairness
AFCA has determined this complaint based on what is fair in all the circumstances, having regard to:
· the legal principles
· applicable industry codes or guidance
· good industry practice
· previous decisions of AFCA or its predecessor schemes (which are not binding).
The respective parties have completed a full exchange of the relevant information, and each party has had the opportunity to address any issues raised. We have reviewed and considered all of the information the parties have provided.
While the parties have raised a number of issues in their submissions, we have restricted this determination to the issues that are relevant to the outcome.
We assess complaints on available information and circumstances
AFCA is not a court of law. We do not have the power to take or test evidence on oath, or to require third parties to give evidence.
When we assess complaints, we consider:
· available documents
· the recollections of the parties
· all relevant circumstances.
We give more weight to documents created at the time the events occurred. If there are no relevant documents, we will decide what most likely occurred based on the available information.
If there are conflicting recollections and these are evenly weighted, we may find that a claim cannot be established.
3.2 AFCA Rules
D.3.3 An AFCA Decision Maker may decide that the Financial Firm is to compensate the Complainant for non-financial loss:
a) for a complaint relating to an individual’s privacy rights - injury has occurred to the Complainant’s feelings or humiliation has been suffered by the Complainant; or
b) for other complaints – an unusual degree or extent of physical inconvenience, time taken to resolve the situation or interference with the Complainant’s expectation of enjoyment or peace of mind has occurred.
3.3 Information from the Guide
Western Australia Guide to standards and tolerances 2019
Introduction
Every year thousands of homes are constructed or renovated in Western Australia. While most building projects are completed successfully, occasionally there may be concerns or unmet expectations that result in a dispute. …… The Guide can be used to help resolve disputes about the quality and standards of work. However, it should be understood that this document is intended as a guide only, all other documents stating statutory and contractual requirements take precedence over this Guide. …
15.08 Levelness of timber floor
New floors are defective if within the first 24 months of handover they differ in level by more than 10mm in any room or area, or more than 4mm in any 2m length. The overall deviation of floor level to the entire building footprint shall not exceed 20mm within 24 months of handover. Refer to Item I of this Guide where the new floor is to adjoin an existing floor
…
Item I Renovations, alterations and extensions
The standards and tolerances in this Guide only apply to the work covered in the relevant home building work contract.
It is recommended that before starting new work, the builder informs the owner of any potential circumstances and conditions of the existing building that may have a detrimental effect on the standard of the new building work.
The builder and owner should agree as part of their home building work contract, or as a written variation to that contract, on the extent of any necessary rectification works that may be required to be carried out to the existing building before commencing that work.
Coded fields were extracted from the text by a language model and may contain errors. The published PDF is the authoritative record.