Claim declined for underground copper pipe leak under corrosion/latent defect exclusion
Text of the determination
Determination
|
Case number
|
12-25-189170
|
Financial firm
|
AIG Australia Limited
Case number: 12-25-189170 28 November 2025
1 Determination overview
1.1 Complaint
The complainant is the trustee of a family trust which held a business insurance policy with the financial firm (insurer). The insured property is a motel and accommodation provider.
On 26 June 2024, the complainant lodged a claim with the insurer following an escape of liquid from underground copper pipework associated with the hot water system at the property. The insurer declined the claim on the basis that a policy exclusion applies because the leaks were caused by electrolysis which led to corrosion of the copper pipe.
The complainant disputes this and wants the insurer to pay the cost of repairing the damaged pipe, reimbursement of increased gas costs and compensation for business interruption.
1.2 Issues and key findings
Is the insurer required to pay the claim?
No. The damage to the underground copper pipes was caused by a defect with the electrical grounding which led to corrosion of the copper pipe. It is therefore excluded from cover. The insurer is entitled to decline the claim in full and is not required to pay any other benefits.
Is the insurer required to cover business interruption?
No. The cover for business interruption is not triggered unless a claim has been accepted or liability admitted for property damage under Section 1.
Why is the outcome fair?
The insurer is entitled to rely on the terms of the policy to determine its liability for the claim. The claimed damage was caused by factors which are excluded under the policy and the business interruption cover does not respond. It is fair for the insurer to decline the claim.
1.3 Determination
This determination is in favour of the insurer.
The insurer is entitled to deny the claim and no further action is required.
2 Reasons for determination
2.1 Is the insurer required to pay the claim?
No. The damage to the underground copper pipes was caused by a defect with the electrical grounding which led to corrosion of the copper pipe. It is therefore excluded from cover. The insurer is entitled to decline the claim in full and is not required to pay any other benefits.
Complainant bears onus of establishing a claimable loss
It is accepted insurance law that the complainant has the initial onus to show, on the balance of probabilities (that it is more likely than not), that the loss or damage claimed falls within the terms of the policy. Where this is established, the onus then shifts to the insurer to prove that an exclusion applies if it seeks to deny or limit its liability for the loss.
There is no dispute that the insurer provided a copy of the policy documents including the Policy Schedule and the Product Disclosure Statement (PDS).
Section 1 of the policy covers accidental physical loss of or damage to the insured property during the period of cover (page 21 of the PDS). The policy also includes an additional benefit for tracing and accessing burst pipes in some circumstances (page 33 of the PDS).
The Policy Schedule lists the period of cover as 13 April 2024 to 13 April 2025.
The complainant lodged a claim with the insurer on 26 June 2024 seeking indemnity for:
· costs incurred to repair water leaks to the underground pipework at the property
· reimbursement of increased gas costs
· business interruption losses due to the interruption of hot water supply to 12 rooms.
The insurer accepts there was a water leak at the property but says there is no physical or structural damage to any property on risk. The insurer also says that the claim is excluded because it was caused by corrosion of the copper pipe.
The question for determination is whether the complainant has established the claimed damage falls within the scope of the policy, or whether it was caused by an excluded peril. This requires consideration of the proximate cause of the loss, being the effective, dominant or operative cause of the loss.
Evidence regarding the cause and extent of the damage
The complainant appointed a plumber (S) who attended the property on 23 June 2024. S identified an issue with the underground hot water line which was causing water leakage. S arranged repairs to the pipework and rendered two invoices for repairs totalling $24,924.37.
S subsequently provided a report which states:
· the leak was sufficient to bring water to ground surface level
· two plumbers completed repairs to the property over a period of 5 days
· the hot water supply to one entire block of accommodation was interrupted
· there would have been substantial LPG loss due to more frequent operation of the heaters
· it is impossible to determine to what degree the hot water unit has been affected
· the original plumbing had been modified, and the electrical earth grounding strap was attached to the original copper cold line above ground which made it redundant
· given the age of the building the copper pipe has deteriorated rapidly
· the repair was done promptly and included all new copper pipework, rectifying the earth stake safety issue, and replacement of the items attached to the copper hot water service
· the failure was not due to lack of maintenance and electrolysis was the cause of the failure.
S provided a further letter dated 16 July 2024 which states that 12 units and the laundry were rendered inoperative for a period of 5 business days from 8 to 12 July inclusive during the repairs. S also noted that sectional cuts of the original pipework were retained to demonstrate the extent and nature of the electrolytic corrosion.
The insurer engaged a loss adjustor (LA) who attended the property on 19 July 2024. LA prepared a report dated 23 July 2024 which states that the complainant noticed ground level water seeping from the ground at the very back of the complex, believed to be coming from underground pipework. A plumber was contacted to assist with addressing the water leak.
The LA report relevantly states:
· S identified that sections of the copper hot water service pipework were corroded and as a result water was seeping into the ground
· the water leaking had not caused any permanent damage to property on risk and was simply ponding on the ground surface without encroaching on any building materials
· extensive plumbing works were undertaken to rectify the leak and upgrade pipework
· the original hot water line is a 32mm copper pipe that runs from the hot water service system underground along the length of the entire western aspect of the complex
· the original hot water line was completely removed, and a new hot water line was installed with isolation valves to allow future isolation of water to individual units
· these works were extensive and were conducted in two stages over a 2-week period
· whilst on site plumbers identified an issue was identified with the hot water unit itself which had exposed pipework noted to be leaking and this was also repaired
· during the repair period 12 accommodation rooms could not be used due to hot water service supply interruption.
Page 3 of the LA report states ‘Plumbers identified the cause of the leaks were from deterioration of the pipes along with some encroachment of tree roots that had impacted around several sections of the underground hot water line pipes.’ However, this is not reflected in the reports by S and there is no other evidence to support this statement.
The complainant says he is unable to provide further evidence from the original plumber as he passed away. He has provided a report by another plumber (M) which states:
· they were unable to respond to an emergency callout on 23 June 2024
· based on their professional assessment the burst pipe and resulting damage appear to be caused by general wear and tear and a poor original design
· no evidence of electrode corrosion was found
· M attended the property to address a similar issue on 20 January 2025 which they were able to resolve before significant damage occurred
· due to design flaws with the original plumbing design, further issues are likely to continue.
Complainant has established a claimable loss
To be covered under Section 1 – Property Damage, the complainant needs to show there was accidental physical loss or damage to the Property Insured at the Situation during the period of insurance.
‘Accidental’ is not defined in the policy. The Macquarie dictionary defines accidental as ‘happening by chance or accident, or unexpectedly.’
‘Property Insured’ is defined on page 11 of the PDS as ‘the property described on the Policy Schedule in respect of each Policy Section. It includes Buildings, Contents, Stock and items listed on the Policy Schedule and used in Your Business or for which you are legally responsible’. The Policy Schedule lists the ‘Situation’ as the name and address of the motel.
There is no dispute that there was a water leak from the hot water pipework at the property during the period of cover. The exchanged information establishes that there was physical damage to the underground copper pipes in the form of pinholes and corrosion, and damage to the exposed pipework on the hot water unit itself which were found to be leaking. I am satisfied this damage happened by chance and was unexpected.
The damaged pipework forms part of the ‘Property Insured’ within the meaning of the policy because it is part of the motel building at the address listed in the Policy Schedule. ‘Building(s)’ is defined on page 7 of the PDS to include ‘underground and above ground services that are Your property or property for which you are responsible and which are connected to any Building…’
It follows that the complainant has established a claimable loss under Section 1 of the policy for the damaged pipework. The cost of any upgrades to the water pipes is not a claimable loss under the policy.
Insurer has established a policy exclusion applies
The insurer relies on the following policy exclusions on page 33 of the PDS:
Exclusions applicable to this Policy Section in addition to the General Exclusions
1.50 We will not cover You for any loss, damage, claim, liability, cost, injury or expense directly or indirectly caused by, arising from or connected with:
(a) corrosion, rust, oxidation, any form of Fungus, wet or dry rot, dampness of atmosphere, variation in temperature, evaporation, disease (in addition to General Exclusion 14 – Disease) or shrinkage;
(b) change in colour, flavour, texture or finish;
(c) inherent vice or latent defect;
The complainant says there is insufficient evidence to show that this exclusion applies. He acknowledges S concluded corrosion was the cause of the damage but says the affected copper pipe was subsequently submitted for laboratory analysis and he was verbally advised by the testing facility that no corrosion was present. He stated this in a letter to AFCA on 21 May 2025 but says no formal report is available.
The insurer has denied commissioning a laboratory analysis of the copper pipe and says neither they nor the LA are aware of such analysis or report. The complainant did not provide further information to support his statement regarding the alleged laboratory analysis.
Having carefully reviewed the available information, I am satisfied on the balance of probabilities that the cause of the damage to the copper pipes for the hot water system was corrosion caused by electrolysis.
The S report states that the copper plumbing in the building was replaced with PVC at some point without adequate provision for electrical grounding. The modification made the electrical grounding strap ineffective, allowing electrical current to pass through the copper pipe, which led to corrosion and eventual failure. No other plausible explanation has been provided for the failure of the pipes at multiple locations.
I am therefore satisfied that the claimed loss and damage falls under the policy exclusions for ‘corrosion’ and/or ‘inherent vice or latent defect’.
I acknowledge the complainant provided a report by another plumber (M). However, I do not consider it persuasive. M did not attend the property at the time of the event and there is no evidence that M inspected the damaged pipe or the property prior to the repairs. I accept the insurer’s position that the M report does not assist the complainant. M attributes the damage to ‘general wear and tear and a poor original design’ which are also excluded causes under section 1.52 of the policy.
For the above reasons, I am satisfied that one or more policy exclusions apply, and the insurer is entitled to decline the claim under Section 1 – Property Damage.
Complainant is not entitled to trace and access costs
Section 1 of the policy includes the following additional benefit on page 33 of the PDS:
1.41 Trace and Access
We will pay the reasonable costs incurred to detect the point of bursting, leaking, discharging or overflowing of fixed apparatus, fixed tanks, fixed appliances, fixed pipes or other systems at the Situation used to hold or carry liquid or gas provided that the bursting, leaking, discharging or overflowing occurred during the Period of Cover and has caused or may reasonably be expected to cause damage to Property Insured. We will also cover the cost of reinstating parts of the Property Insured necessarily disturbed to locate the source of the problem.
Provided that we will not cover the cost of repairing or reinstating any such apparatus, appliance, tank or repair which has failed due to age, wear and tear, faults in material or faulty workmanship by the installer.
The insurer says this policy benefit does not apply because the leak was easily identified without need to investigate and therefore no costs were incurred to trace the leak/s. In addition, the LA report states water ponding from the leaking pipes into and onto ground surface (lawn) could not encroach on any property on risk.
Based on the exchanged material, I am satisfied the complainant incurred costs engaging a plumber to detect the point of leaking from fixed pipes at the property which may reasonably be expected to cause damage to the Property Insured. This is because:
· it is well known that water escaping from a leaking pipe may cause damage to nearby buildings if not addressed
· it is reasonable to expect that a water leak may cause further damage to the pipework or attached fixtures (including the hot water unit) if not addressed.
I therefore consider the first part of the ‘Trace and Access’ benefit is satisfied. However, the complainant has not provided evidence of the reasonable costs associated with detection of the issue (such an itemised invoice from S).
Further, the benefit includes a specific exclusion for the cost of repairing any apparatus ‘which has failed due to age, wear and tear, faults in material or faulty workmanship by the installer’. It is also subject to the exclusions of the policy (see page 28 of the PDS).
Based on the expert evidence and my finding that the claim under Section 1 is excluded, I am satisfied that any leak detection costs incurred by the complainant are also excluded. The insurer therefore is not required to pay any ‘Trace and Access’ costs.
Complainant is not entitled to increased gas costs
The complainant has provided an LPG bill dated 31 July 2024 which he says shows an increase in gas usage from $2,395.52 in June to $3,517.92 in July. He wants the insurer to reimburse the increased costs and relies on a letter from S in support of this.
I acknowledge the water leak may have caused an increase in LPG usage. However, the insurer is not required to cover this because:
· the insurer is entitled to decline the claim under Section 1 entirely, and it therefore is not required to pay for any loss or damage arising from the incident
· the policy excludes any kind of consequential or indirect loss under the General Exclusions on page 18 of the policy.
2.2 Is the insurer required to pay for business interruption?
No. The cover for business interruption is not triggered unless a claim has been accepted or liability admitted for property damage under Section 1.
Complainant seeks business interruption losses
The exchanged material shows that there was a period of approximately 2 weeks where 12 accommodation rooms could not be used by customers due to hot water supply interruption while the leaking plumbing was repaired and upgraded.
The complainant claims loss of gross profit arising from the interruption to the accommodation usage and estimates gross revenue loss to be approximately $16,000.00 including GST. The LA reported that gross profit loss may be in the vicinity of approximately $6,000.00 including GST, but no detailed calculations were made.
The insurer acknowledges the complainant had to repair the damaged pipework, and the water supply was interrupted during these works, which resulted in some rooms being unavailable. However, it says for the cover under Section 2 – Business Interruption to trigger there must be a coverable event from Section 1 – Property Damage.
Insurer is not required to cover business interruption
The policy includes optional cover for Business Interruption under Section 2. Page 36 of the PDS states ‘This Policy Section only forms part of Your Policy when Business Interruption is shown in the Policy Schedule’.
The Renewal Policy Schedule issued on 30 May 2024 states ‘Business Interruption Not Taken’ under the relevant property. However, an Endorsement Policy Schedule was issued effective 6 June 2024 which states ‘Business Interruption Taken’ under the relevant property.
I am satisfied the complainant had cover for Business Interruption at the time of the event on 23 June 2025. However, the cover under Section 2 is not triggered unless a claim has been accepted or liability admitted for property damage under Section 1.
Given I have already found that the insurer is entitled to decline the claim under Section 1, the insurer is not required to pay for any business interruption losses.
2.3 Why is the outcome fair?
The insurer is entitled to rely on the terms of the policy to determine its liability for the claim. The claimed damage was caused by factors which are excluded under the policy and the business interruption cover does not respond. In the circumstances, it is fair for the insurer to decline the claim.
3 Supporting information
3.1 The AFCA process
AFCA’s approach is based on fairness
AFCA has determined this complaint based on what is fair in all the circumstances, having regard to:
· the legal principles
· applicable industry codes or guidance
· good industry practice
· previous decisions of AFCA or its predecessor schemes (which are not binding).
The respective parties have completed a full exchange of the relevant information, and each party has had the opportunity to address any issues raised. We have reviewed and considered all of the information the parties have provided.
While the parties have raised a number of issues in their submissions, we have restricted this determination to the issues that are relevant to the outcome.
We assess complaints on available information and circumstances
AFCA is not a court of law. We do not have the power to take or test evidence on oath, or to require third parties to give evidence.
When we assess complaints, we consider:
· available documents
· the recollections of the parties
· all relevant circumstances.
We give more weight to documents created at the time the events occurred. If there are no relevant documents, we will decide what most likely occurred based on the available information.
If there are conflicting recollections and these are evenly weighted, we may find that a claim cannot be established.
Coded fields were extracted from the text by a language model and may contain errors. The published PDF is the authoritative record.