Insurer declined claim for wall cracking said to be caused by its repairer's drying equipment; minor re-repairs agreed and non-financial loss awarded
Text of the determination
Determination
|
Case number
|
12-24-164411
|
Financial firm
|
RACQ Insurance Limited
Case number: 12-24-164411 30 June 2025
1 Determination overview
1.1 Complaint
The complainant held a home building and contents policy with the financial firm (insurer). The complainant lodged claims on 16 September 2022 for damage to the roof (sagging) and on 16 May 2023 for internal mould arising from the roof sag. The claims arose from repairs performed by the insurer’s repairers after it had accepted claims for cyclone damage in 2006 and 2011.
The complainant made a previous complaint to AFCA about the roof sagging and internal repairs. Both the complainant and the insurer accepted a Recommendation by AFCA (981958) dated 30 October 2023. The AFCA Recommendation required the insurer to rectify the repairs by authorising further repairs or cash settling the repairs.
The complainant lodged a further claim with the insurer on 8 October 2024 and a further complaint with AFCA on 4 November 2024. The complainant said that the insurer’s repairer had caused further damage to the complainant’s home (wall cracking) which required additional repairs and for damage to the carpet. The insurer denied that it was required to repair the wall cracks. The parties have resolved the issue regarding the carpet.
The insurer has also agreed to perform minor painting and re-repairs which were not properly performed (but not to perform repairs to the wall cracks).
1.2 Issues and key findings
Was the insurer entitled to decline the claim for cracking damage to the walls?
Yes. The insurer has correctly declined the claim for cracking damage to the walls.
Was the insurer obliged to repair the cracking damage under the lifetime guarantee?
No. The insurer was not obliged to repair the cracking damage under the lifetime guarantee.
Has the insurer correctly assessed the minor painting and re-repairs?
Yes. The insurer has correctly agreed to perform minor painting and re-repairs.
Is the complainant entitled to non-financial loss compensation?
Yes. It is fair for there to be an award of non-financial loss compensation.
Why is the outcome fair?
The outcome is fair because it is fair and appropriate for the insurer to perform the minor painting and re-repairs (but not to the wall cracks). It is fair for the insurer to pay an award of non-financial loss compensation.
1.3 Determination
This determination is substantially in favour of the insurer.
Within 28 days of receiving notice of the complainant’s acceptance of the determination, the insurer shall:
· if it has not already done so, appoint a repairer to complete the minor painting and re-repairs set out in section 2.1 at the insurer’s cost
· pay the complainant $3,000 in non-financial loss compensation
Further, upon the complainant’s acceptance of this determination:
· upon the appointment of the insurer’s repairer, the complainant shall provide access to the complainant’s property to enable the insurer’s representatives to conduct the minor re-repairs until their completion
2 Reasons for determination
2.1 Was the insurer entitled to decline the claim for cracking damage to the walls?
Yes. The insurer has correctly declined the claim for cracking damage to the walls.
Policy covered accidental damage subject to exclusions
It is established insurance law that the complainant has the onus to establish the claimed loss is a result of an event covered under the policy during the period of insurance. This must be established on the balance of probabilities, meaning that it is more likely than not.
The terms and conditions of the policy are set out in the Products Disclosure Statement (PDS) and the Certificate of Insurance (COI).
The initial onus is with the complainant to establish on the balance of probabilities (that is more likely than not) that the loss or damage claimed falls within the insuring provision of the policy.
If the complainant establishes a valid claim, the onus shifts to the insurer to establish, on balance, it is entitled to rely on an exclusion under the policy or is otherwise entitled to decline the claim.
The relevant cover under the policy included loss or damage to the complainant’s home caused by accidental damage. ‘Accidental damage’ was defined in the policy as damage caused by an accident. The expression ‘accident’ was defined as
‘an event or incident which you did not intend or expect’.
The policy contained general exclusions including ‘general deterioration’ and ‘wear and tear’.
Complainant said that damage had been caused by insurer’s repairer
The damage which the complainant said the insurer’s representatives had caused was due to work which the complainant and the insurer had agreed that the insurer would perform based on an earlier Recommendation by AFCA. The earlier Recommendation by AFCA was dated 30 October 2023 and required the insurer to:
· appoint C or another engineer to prepare a SOW to rectify the repairs to the roof. The SOW should also include repairs to the skylight and dek-tites
· engage a hygienist to prepare a SOW for mould remediation
· either authorise a repairer to repair the roof and treat the mould or settle the claim based on an actionable quote
· if the insurer chose to cash settle the claim, the insurer was required to include a 20% contingency if it was not already included.
The complainant and the insurer agreed to the Recommendation and sought to implement its terms. On 8 October 2024, the complainant said that the insurer’s representatives had caused damage the walls, architraves and windowsills due to the use of drying equipment for an extended period.
Insurer’s experts said wall cracking was not caused by the insurer’s repairer
The insurer engaged the repairer, DR, to prepare a report on 16 October 2024 that said:
· all cracks in walls were evident in initial inspection photos and had not been damaged during restoration
· equipment was not placed in the house to dry the building and minimal equipment was used during restoration for environmental stabilisation
· HEPA Air Scrubbers and air movers were predominantly used, with 'minimal' dehumidification during the days where the ceilings and walls were washed
· photographs taken prior to any works being undertaken showed cracks on walls throughout
· damage had not been caused during restoration.
The insurer also engaged its property assessor, IP, to prepare a report based on an inspection on 22 October 2024. IP said:
· the walls were cladded with 4.6 mm Masonite sheets which was naturally prone to movement
· the cracking was spasmodic, occurring in some but not all rooms, and affecting 1 or 2 walls but not all walls
· the insurer’s restoration had not caused the internal wall cracking, as the cracking would be more extensive and consistent in all rooms
· wall cracking was more consistent with natural building movement
· the insurer should engage an engineer to provide an independent report.
The insurer then engaged AB, builder, to prepare a report dated 30 October 2024. AB said:
· movement/ settlement cracking to the wall cladding was isolated to the sheet joins
· there was no cracking to the plasterboard ceiling or cornice
· rear right hand side bedroom was the most noticeable room with cracking but there was no cracking to the plasterboard ceiling or cornice but only to the Masonite wall lining at the joins
· there was paint peeling in the robe of the front RHS bedroom which was due to poor preparation prior to paint application
· an active leak was observed to be coming from a failed toilet pan seal in the WC and appeared to be tracking though the wall and affected the carpet in the bedroom adjacent.
· the internal cracking was a result of excessive drying of the structure
· it was ‘plausible the internal cracking is a result of excessive drying of the structure’
· the insurer should review whether the internal cracking was related to movement/settlement over time or excessive drying of the structure, affecting the Masonite wall linings
The insurer engaged CR, an engineer, to prepare a report dated 1 November 2024. CR set out detailed observations regarding the properties of Masonite, the size and nature of the cracks, historical repairs and the remediation works performed. CR noted that equipment used was ‘a HEPA Vacuum, specialist equipment for Environmental Stability, and a ULV fogging machine’ and that none of that equipment had ‘a heating or drying nature that would result in loss of Equilibrium Moisture Content (EMC) of the building materials’.
CR concluded:
· the original tempered Hardboard (Masonite) was not manufactured to enable an applied filler to be inserted; typically, the use of applied fillers to provide an even or smooth surface was applied to material such as plasterboard or Villa-board which both are manufactured with either a tapered or recessed edge, as they are designed to accept a base coat, tape and top coat to obtain a resilient joint covering
· the cracking in the retained V jointed Masonite was merely that of a hairline crack in the paint, whereas the filled V joints displayed a more amplified appearance due to the thickness of the filler or its displacement from the joint
· historical repairs and current repairs had occurred onsite well prior to any form of reinstatement or remedial works being undertaken
· the actions of the insurer’s representatives had not resulted in any claimed cracking of the sheeting, and to support CR’s opinion, the plasterboard ceilings subjected to the same works, did not contain any damage that would support or reflect the cracking as seen in the Masonite
· the cracking observed was regarded as cosmetic, and both historical and ongoing, and therefore replacement was not required
Complainant’s expert said the insurer’s repairers caused the damage
The complainant engaged an expert, PI, a builder and residential building inspector, to prepare a report based on an inspection on 14 February 2025. PI concluded that the shrinkage cracking had been caused by the recent restoration works but PI provided no assumptions, basis or reasoning for the conclusion reached.
PI provided a second report at the complainant’s request on 15 February 2025. PI stated:
· Masonite Standard was a wood fibre building board, manufactured in Australia to comply with the requirements for Standard Hardboard, type GP in Australian Standard AS2458-1982. Masonite Standard is intended for dry area, interior use - commonly used as wall and ceiling linings up until the early 1980’s
· prior to installation, Masonite was moisture conditioned on site by brushing water onto the rear face of the boards and leaving them for 24hrs to condition to the atmospheric relative humidity of the site
· Masonite wall lining had a hygro-expansivity of 0.25% in relative humidity of 50%-90%. Hygro-expansivity referred to the tendency of a material to expand or contract in response to moisture content
· according to the Australian Bureau of Meteorology, where the property was located had a mean annual relative humidity of 62%. September was the month with the lowest relative humidity at 55%
· over the course of a normal year, the Masonite lining board maintained its moisture content and its hygrometer-expansivity at a stable level. Shrinkage and expansion did not occur
· the Masonite wall linings had been flush set by a plasterer approximately 10 years ago. The wall linings had remained stable and no cracking was present prior to 2024
· following the usage of 13 drying machines (a combination of fans and dehumidifiers) that were left running in the house for approximately 4 weeks. The relative humidity of the home had been reduced to below 50% and shrinkage had occurred. The shrinkage had caused cracking at the sheet joints
· the rooms inspected showed clear signs of shrinkage cracking to the wall linings, architrave mitre joints and cornices
· a review of images prior to the restoration works confirmed that the shrinkage cracks identified were not present prior to the restoration works
· the shrinkage cracking had been caused by the recent restoration work
In response to PI’s second report, the insurer engaged CR to provide a Supplementary Report dated 20 March 2025. In the preparation of CR’s Supplementary Report CR reviewed in detail the documents which had been logged with the insurer by the remediation contractors (CH and DA) and contacted CH and:
confirmed that 13 items of mechanical restoration equipment were stored on site in readiness for use as required, however, not all were utilized or operational during the works, and that the equipment was not left running for 4 weeks as stated by the [the complainant]. [CH] again reinforced the use of some equipment was to maintain environmental stability due to wet wiping only; and that no heat generated drying was undertaken
CR concluded:
· the two previous reports were supported by images as taken by CH prior to remediation works being undertaken in 2024
· the CH images clearly showed the complainant’s contents were still onsite and the cracking to the sheet joins was clearly visible in numerous locations throughout the property
· the use of fans, dehumidifiers and air scrubbers was to maintain environmental stability; in other words, to maintain the existing relative humidity conditions with the property during wet wipe works to remove and sanitize the surface mould on painted surfaces
· the reports provided by PI provided no evidence such as before and after comparative images and were not substantiated
· the Masonite sheeting does experience expansion and contraction during changes in relative humidity, which had been an ongoing occurrence within the property since construction. The application of an unapproved filler 10 years prior to the event had been subjected to the same expansion and contraction movements, which presented as hairline to 0.25mm crack lines in the sheet joints
· the cracking was also visible in the unfilled yet painted joints as seen in the robes, which had presented itself as hairline to 0.25mm cracks in the numerous layers of applied paint over 30+ years.
· PI’s opinion that repair to the wall sheet joints to be in the form of full wall sheet replacement was a proposal which was ‘extreme and unwarranted’
· the application of a plastering filler was not compliant with the Masonite Standards of 1991, the complainant had engaged persons unknown some 10 years prior and was accepting of its performance
· as referred to in his first report, a like for like repair (clean out of joints and reapplication of filler) followed by painting would resolve the issue, however, contractors engaged by the insurer would not be able to provide a warranty for the works, due to underlying issues with historical painting.
The insurer is entitled to decline the claim
Based on the information, the complainant has established a valid claim for accidental damage, subject to the operation of the exclusions under the policy. This is because the complainant noticed damage to the property that was unintended and unexpected from her point of view.
Given the complainant has established a valid claim, the onus shifts to the insurer to prove, on the balance of probabilities, it can decline the claim based on an exclusion in the policy.
The insurer’s experts say that the cracking damage was pre-existing and is therefore excluded under the policy. This was supported by photographic evidence that shows cracks existed before the insurer’s contractors undertook repairs after the parties reached the previous agreement. It also shows that there have been historical repairs to the Masonite boards prior to the previous claim.
The opinions in the two reports by the insurer’s expert, CR, an engineer, were supported by its detailed observations, the size and nature of the cracks, the evidence of historical repairs and nature of the remediation works which had been performed by the insurer’s repairer.
Based on the information, CRs’ opinions are, accordingly, more persuasive and are to be preferred. The insurer was, accordingly, entitled to decline the claim based on the exclusions for general deterioration and wear and tear which were the cause of the cracking to the walls, and that these cracks were pre-existing.
2.2 Was the insurer obliged to repair the cracking damage under the lifetime guarantee?
No. The insurer was not obliged to repair the cracking damage to the walls under the lifetime guarantee.
Works carried out by the insurer are subject to a lifetime guarantee
Alternatively, the complainant said that the insurer was liable for the cracking damage under the lifetime guarantee because the insurer’s repairer caused the cracking damage when completing the repairs and using the drying equipment.
The insurer was obliged under the lifetime guarantee to fix any faulty workmanship if the complainant made a claim (and still owned the home) and if the repairs were completed by the insurer’s authorised repairer. The lifetime guarantee did not cover repairs because of wear, tear and gradual deterioration or movement of the complainant’s home.
Based on the information, for the same reasons (set out above) that the insurer was entitled to deny the claim under the policy, the insurer was not obliged under the lifetime guarantee to repair the wall cracks. There was no faulty workmanship by the insurer’s repairer and the cracking to the walls arose because of wear, tear and gradual deterioration and movement of the complainant’s home which was excluded under the lifetime guarantee.
2.3 Has the insurer correctly assessed the minor painting and re-repairs?
Yes. The insurer has correctly agreed to perform minor painting and re-repairs.
The insurer’s offer to complete further repairs is fair and reasonable
On 19 June 2025 the insurer agreed that minor painting and re-repairs are to be performed. Those items to be re-repaired were:
· poor painting to the left front corner with a paint run on the beam
· paint to the soffits had debris in the paint
· trim covering junction between soffit and brick to be replaced
· appearance to the soffit between the old and the new soffit
· paint over-run on the edge of the fascia
· defects which had been stickered but not repaired to the side of the home
· gaps on the rear soffit behind the shed
· inconsistent nail fixings to the patio ceiling with some nails having been hammered below the surface to be filled and repainted
· gap between the brick and patio ceiling to be resealed
· scratch to the underside of the gutter to be repaired
· gutter end cap to be reduced
· cracks to the trims of the two skylights to be rectified
It is fair and appropriate that the insurer perform the above repairs if it has not already done so. Upon the appointment of the insurer’s repairer, the complainant shall provide access to the complainant’s property to enable the insurer’s representatives to conduct the minor re-repairs until their completion.
2.4 Is the complainant entitled to non-financial loss compensation?
Yes. It is fair for there to be an award of non-financial loss compensation.
AFCA can award compensation for non-financial loss
This complaint was lodged with AFCA on 4 November 2024. Under AFCA’s Rules, AFCA can award up to $6,300 compensation for non-financial loss in relation to a complaint lodged after 1 January 2024. This must relate to poor claims handling or other actions of the insurer which cause an unusual degree of stress, delay, or inconvenience.
Insurer must pay non-financial loss compensation
In accordance with what is fair in all the circumstances, I determine the insurer must pay the complainant $3,000 compensation for non-financial loss.
In the circumstances of the complaint, it is not productive, and not fair to the parties, to traverse each aspect of the protracted claims history and the extensive number of communications. The insurer’s claim notes recorded that there were over 300 pages of notes between the earlier AFCA Recommendation dated 30 October 2023 (981958) and 17 February 2025. It is fair and appropriate to seek to progress the resolution of the complaint and the claim, including a fair assessment of non-financial loss compensation.
Based on the information, the complainant has experienced extensive inconvenience. On 20 February 2025 the insurer made an ex gratia offer of $2,500 to resolve the complaint but that offer was not accepted by the complainant. The complainant will also experience further inconvenience during the period in which the minor repair works are conducted. The insurer is not required to conduct repairs to the cracking to the walls. A significant amount of the communications between the complainant and the insurer related to that issue which has not been determined in the complainant’s favour.
In the circumstances, it is fair for the insurer to pay the complainant $3,000 in non-financial loss compensation.
2.5 Why is the outcome fair?
The outcome is fair because it is fair and appropriate for the insurer to perform the minor painting and re-repairs (but not to the wall cracks). It is fair for the insurer to pay an award of non-financial loss compensation.
3 Supporting information
3.1 The AFCA process
AFCA’s approach is based on fairness
AFCA has determined this complaint based on what is fair in all the circumstances, having regard to:
· the legal principles
· applicable industry codes or guidance
· good industry practice
· previous decisions of AFCA or its predecessor schemes (which are not binding).
The respective parties have completed a full exchange of the relevant information, and each party has had the opportunity to address any issues raised. We have reviewed and considered all the information the parties have provided.
While the parties have raised a number of issues in their submissions, we have restricted this determination to the issues that are relevant to the outcome.
We assess complaints on available information and circumstances
AFCA is not a court of law. We do not have the power to take or test evidence on oath, or to require third parties to give evidence.
When we assess complaints, we consider:
· available documents
· the recollections of the parties
· all relevant circumstances.
We give more weight to documents created at the time the events occurred. If there are no relevant documents, we will decide what most likely occurred based on the available information.
If there are conflicting recollections and these are evenly weighted, we may find that a claim cannot be established.