Denial of storm damage claim to roof and ceiling; claimed damage not shown to be caused by a storm, plus non-financial loss for protracted claim handling
Text of the determination
Determination
|
Case number
|
12-00-1031893
|
Financial firm
|
AAI Limited
Case number: 12-00-1031893 21 March 2025
Determination overview
Complaint
The complainant holds a home and contents insurance policy for his home in Victoria with the financial firm (insurer). The policy period was from 4 April 2021 to 4 April 2022. The building cover was $629,100 and the contents cover was $224,000.
The complainant made a claim on 2 May 2021 for storm damage to the complainant’s home which the complainant said occurred on 11 April 2021.
The insurer denied the claim on 30 November 2021.
The complainant made a complaint to the Australian Financial Complaints Authority (AFCA) (AFCA complaint 865258). During the course of that complaint on 19 July 2022 the insurer agreed to re-assess the claim in accordance with the policy.
On 24 July 2023 the insurer declined the claim and said that the complainant had not established that an insured event had caused the damage claimed. Alternatively, the insurer said the claim was excluded.
The complainant made a further complaint to AFCA on 29 October 2023 and said that the insurer should not have declined the claim. The insurer maintained its denial on 30 November 2023.
Issues and key findings
Is the insurer entitled to deny the claim?
Yes. The insurer is entitled to deny the claim as the complainant has not established a valid claim.
Is the complainant entitled to non-financial loss compensation?
Yes. In the circumstances, an award of non-financial loss compensation is warranted.
Why is the outcome fair?
The outcome is fair because the insurer is entitled to rely upon the exchanged material and the terms and conditions of the policy to determine its obligations regarding the claim.
Determination
The determination is in favour of the insurer.
Within 14 days of receiving notice of the complainant’s acceptance of the determination, the insurer shall pay to the complainant $2,000 for non-financial loss.
Reasons for determination
Is the insurer entitled to deny the claim?
Yes. The insurer is entitled to deny the claim as the complainant has not established a valid claim.
Coverage of the policy
The complainant’s home and contents insurance policy provided cover for loss or damage caused by insured events during the period of insurance. The coverage provided by the policy is subject to conditions, limitations, and exclusions. This means that not all loss and damage is automatically covered. Rather, only loss and damage caused by an insured event, during the period of insurance and subject to the conditions, limitations and exclusions, is covered.
The full details of the policy coverage, conditions, limitations, and exclusions are contained within the Product Disclosure Statement (PDS) and Certificate of Insurance (COI) (together referred to as the policy).
I am satisfied that the PDS and COI have been provided to the complainant. Therefore, the insurer is entitled to rely upon the terms of the policy, including its conditions, limitations, and exclusions, to determine its obligations to the complainant
Complainant has initial onus to establish a valid claim
The initial onus is with the complainant to establish on the balance of probabilities (that is more likely than not) that the loss or damage claimed falls within the insuring provision of the policy. This is known as a ‘valid’ (or prima facie) claim.
Once the complainant has established a valid claim, the onus shifts to the insurer to establish, on balance, the application of a policy exclusion or that it is otherwise entitled to decline or limit the claim under the policy.
Proximate cause
When establishing the cause of the damage to the complainant’s property, it is the proximate cause that must be established. The proximate cause is not necessarily the first or the last or the sole cause of the damage. It is the dominant or effective or operative cause. The proximate cause of the loss is a question of fact to be determined based on the circumstances. Where there are several causes operating, each must be considered to determine its impact on the resultant damage or loss. If one cause results in the loss or damage in any case, and the other would not without the first, the first is the proximate cause. A common-sense approach is taken to determine proximate cause.
Policy covered loss or damage to building and contents caused by storm
There is no dispute that the policy held by the complainant covered ‘loss or damage caused by a storm’ (page 22). Storm was defined (page 105) as ‘a storm, cyclone or severe atmospheric disturbance. It can be accompanied by strong winds, rain, lightning, hail, snow or dust’.
The policy provided (page 87) that the complainant needed to ‘prove that an incident covered by your policy actually took place. If you do not do this, we will not be able to pay your claim’.
The policy defined ‘Incident or event’ (page 103) as meaning:
a single event, accident or occurrence which you did not intend or expect to happen that is not excluded by your policy. A series of incidents attributable to one source of originating cause is deemed to be the one incident.
Policy contained exclusions
The policy contained an exclusion (page 78):
Loss or damage to, or caused by, connected with or arising from, or liability caused by, connected with or arising from:
Home, unit or contents not in good condition
any part of the home, unit or contents not being in good condition, such as, but not limited to:
• the roof leaks when it rains;
• there are blocked gutters;
The policy also contained this exclusion (page 81):
Loss or damage to, or caused by, connected with or arising from, or liability caused by, connected with or arising from:
Wear, tear, mould, gradual deterioration and other conditions
any part of the home or contents that has wear, tear, rust, fading, rising damp, mould, mildew, corrosion, rot, action of light, atmospheric or climatic conditions or gradual deterioration such as, but not limited to:
• tiles and their adhesive or grouting breaking down;
• weathering of roof tiles or roof ridge capping;
• gradual weathering and breakdown of bricks, mortar or concrete;
• fading of curtains and drapes;
• gradual weathering of pot plants;
• wear and tear of carpets, furniture and furnishings;
• gutters rusted after exposure to the elements
Complainant made a claim for storm damage which was denied by the insurer
The insurer agreed on 19 July 2022 to reassess its initial denial of the claim. On 24 July 2023 the insurer declined the claim and maintained its denial on 30 November 2023.
The complainant made a further complaint to AFCA on 29 October 2023 and said that the insurer should not have declined the claim. On 19 December 2023 the complainant said that:
[the insurer’s] excuse for the roof “not being compliant” has been proven in the past claim in 2010 that it actually is compliant... the structure was built and compliant by the [Victorian Building Authority] many years ago. Fact that every event / claim has only ever happened when there has been a “natural disaster” / “storm” proves the point that it is inevitable.
The reference by the complainant to ‘every event/ claim’ alludes to earlier claims which had been made by the complainant. On 12 March 2024 the complainant advised AFCA that ‘Regarding the events claimed from 2010 to current all incidents that have and did occur have been at various separate positions and location on the property. The damages or events never were at the same location which would highly indicate it is a separate incident.’ It is important to emphasise that this Determination relates only to the claim made by the complainant for storm damage which the complainant said occurred on 11 April 2021 and is the subject of the policy between the complainant and the insurer for the policy period from 4 April 2021 to 4 April 2022.
Insurer engaged experts regarding the cause of the damage
After the claim was made, the insurer engaged the following experts:
S, plumber, who prepared a Roof Report based on an inspection on 12 August 2021 (5 pages with supporting photographs)
J, builder, who prepared an assessment report based on an assessment on 12 August 2021 (2 pages with supporting photographs).
H, consulting engineers, who prepared an engineering and inspection report dated 9 September 2021 (based on a site inspection on 1 September 2021) (19 pages with supporting photographs)
M, engineers and building consultants, dated 13 July 2023 (based on an inspection on 20 June 2023 along with16 pages of supporting photographs)
S’s Report was based on an inspection of the roof. S found:
the rear living room was an extension from the original house
> the original squareline gutter was never upgraded to a box gutter
> as a result, the gutter which was located between the existing house and the extension was now an internal gutter which was under sized and did not comply with Australian standards
there was the potential this gutter could quite quickly fill up with water and overflow. If it were to overflow it would overflow back into the property
there was no clear evidence that the gutter had overflowed at that time but recommended the square line gutter be upgraded to a box gutter that complies with Australian standards to ensure the gutter does not overflow in the future and cause any possible damage to the property
the laps on the roof sheets directly above the damaged room had been silicone sealed together which was a good indication that there have been an ongoing issues with this particular roof for several years
there was no sisalation paper below the roof sheets, and as a result of this, condensation water had been dripping off the sheets into the ceiling space over several years and has caused the main extent of the damage found right through the ceiling space
sisalation paper needed to be installed, which needed to then run into the gutter to prevent condensation water from leaking into the ceiling space
the top apron flashing was under size and did not comply with Australian standards as the apron flashing should be 250mm wide but was only 125mm wide
the flashing had not been secured to every rib of the roof sheets and it was therefore not secured correctly. Due to this, wind driven rain has a high chance of being blown up and over the tops of the roof sheets into the ceiling space below which would have been another contributing factor
water would be seeping through the seals into the ceiling space and would be another contributing factor
S made the following conclusions and recommendations:
there was no evidence of any storm damage to the roof
all the internal damage had been caused over a long period of time due to a combination of maintenance issues and building defects only
there is no sisalation paper underneath the roof sheets and, as a result of this, condensation water had been dripping into the ceiling space over several years and had caused a large extent of the damage found
the top apron flashing was under size and did not comply with Australian standards. As a result of this wind driven rain had been blown up and over the tops of the roof sheets into the ceiling space where it has spread across the ceiling and has contributed to the damage
the silicone seals around the heating flue have signs of deterioration where further water can now seep through into the ceiling space and be another contributing factor
a combination of these issues had caused the damage found
there were further areas of concern with the roof that may cause further damage in the future as S found the existing square line gutter was never removed and replaced with an internal box gutter when the house was extended. As a result of this, the squareline gutter, which is now an internal gutter, can potentially build up and overflow back into the property and cause a large extent of damage. Due to this, the gutter needed to be upgraded to a box gutter with a sump and overflow provision to ensure it will not build up and overflow back into the property and cause any possible damage in the future
recommendations:
> install sisalation paper below the roof sheets above the rear living area to prevent further condensation water leaking into the ceiling space below
> upgrade the apron flashing along the top of the roof to a minimum of 250mm wide, to ensure that wind driven rain does not get blown up and over the tops of the roof sheets.
> ensure the apron flashing is secured to every rib of the roof sheets to ensure that it is secured correctly
> reseal the heating flue penetration to ensure that it is watertight.
maintenance issues not related to the internal damage of the rear living room ceiling
> upgrade the existing square line gutter to a box gutter with a sump and an overflow to ensure the gutter cannot build up with water and overflow back into the property
J’s Report concluded that the damage sustained was a result of maintenance on the roof that had occurred over a long period of time and repeated the conclusions and recommendations in S’s Roof Report.
H’s Report contained:
Internal Photograph (Figure 21) ‘Seam separation and previous repair attempts to ceiling of living room’
Internal Photograph (Figure 22) ‘Point of water ingress – area directly below blocked downpipe – Significant cracking to ceiling of living room – Previous repair attempts to ceiling also evident’
H’s Report stated in the section: ‘What caused water ingress through the roof?:
According to the National Construction Code (NCC) – Vol: 2 part 3.5, regarding roof cladding, weatherproofing of roofs is one of the major defective aspects of building work and defective roof flashing systems are a common cause of water penetration in roofs. It is essential to install a complete flashing system that intercepts, collects, and discharges moisture or water back on to roof stormwater drainage system.
An inspection of the roof revealed points of un-weatherproofed areas and failed sealing attempts. This allows water to enter the roof through wind-driven rain and capillary action. There was also evidence of blocked roof gutter and water ponding at the roof gutter which allows water to overflow from the gutter and enter into the roof cavity. The water ingress that had occurred and damage to the ceiling is a direct result of rainfall that was able to enter the house through gaps in the roof through various rainfall periods.
The available evidence indicates that water had entered the roof cavity due to the poor condition of the roofing causing the observed water staining during rainfall events. The water ingress was attributed to a lack of effective maintenance/moisture protection over a prolonged period. It was apparent that the roof had sustained long-term deterioration and subsequent ingress issues in many locations before the recent event, as evidenced by previous repair attempts. Thus, the damage is not attributable to the isolated event.
M's Report stated:
the non-compliant and poorly constructed roof had resulted in the purported water entry into the home on two separate recorded event occasions
the non-compliant and poorly constructed roof had been allowing moisture entry into the home over a long period of time and is continuing to do so
the water entry into the home was a long-term and ongoing issue as a result of the non-compliant construction of the roofing
at the time of M’s inspection, the replacement of roof sheeting and patching to the roof was observed
the ‘Proximate Cause and Effect’
> the roof is of a non-compliant construction and does not meet the minimum requirements of AS3500.3, installation codes and guidelines
> the non-compliant roofing construction and deteriorated condition allowed for long term water entry and leaks into the home and cavities and was not as a result of any one single event
> ongoing water entry and moisture related deterioration would continue to develop in the absence of appropriate roofing upgrades and reconstruction
Complainant engaged experts
After the claim was made, the complainant engaged the following experts:
B, builder, letter (2 pages) dated 5 June 2022
N, builder, letter (1 page) dated 9 June 2022
N, builder, letter (3 pages) dated 22 November 2024
B’s letter dated 5 June 2022 stated that he had been engaged to look at the cost of works to be undertaken at the complainant’s property to fix and rectify water damaged areas. B provided a quotation dated 17 June 2021 which contained a scope of works in the amount of $37,590 (excl GST) for labour and materials. However, the quotation contained no information regarding the cause of the damage to the complainant’s home. B stated in B’s letter:
• From the photos [in H’s Report] showing maintenance was the cause on the roof show old silicone and roof sheets had been patched. Well yes there is silicone visible and yes it has discoloured as does all clear silicone in direct sunlight but silicone is used on all aspects of roofing under flashings etc etc as a 2nd barrier.
• Also patching a roof sheet on a clip lock style roof is done the way shown in the photo hence the same way when fitting a skylight or a venting system you cannot just replace on sheet without pulling the entire roof off as start one side and work across hence it’s a clip lock system.
• Rotted fascia was also noted on the list of maintenance clearly not rotted but flaky paint if inspected correctly.
[B’s opinion was] that the property should have be covered thru insurance as it is clearly visible that it was from storm damage. Not from poor maintenance as [the complainant] was advised when his claim was rejected as the house isn’t a brand new dwelling yet a existing home and if you inspect a number of existing homes you’ll find the similar issues not poor maintenance.
The conclusion by B that it was ‘clearly visible that [the damage] was from storm damage’ was not supported by any reasoning or by any reference to photographic or other information. Further, the reference by B to the complainant’s home not being brand new and that other existing homes may have similar issues was a generalisation. It was not of any assistance to the complainant regarding the cause of the damage to his home. In those circumstances, B’s letter is of very little weight and is not supportive of the complainant’s claim that storm damage occurred on 11 April 2021.
N’s letter dated 9 June 2022 stated that N had reviewed H’s report dated 9 September 2021. N stated:
H’s report’s conclusion that the property is of fair condition for its age was ‘a reasonable assessment’
N had not undertaken a site visit
H’s report failed to give ‘adequate reference to the location of supposed maintenance issues in relation to the leak’ or ‘provide adequate evidence to identify the cause of the leak’
H’s report sought ‘to undermine the maintenance history of the property, which is very difficult to ascertain, and [H’s] commentary appears to be subjective’
the property was not in a state of disrepair as suggested by H
As acknowledged by N, the letter by N dated 9 June 2022 was not prepared based on a site inspection by N. N’s conclusions, which purported to concentrate on challenging H’s conclusions, were not based on any assessment by N in which N addressed the cause of the damage at the complainant’s home. In those circumstances, N’s letter is of very little weight and is not supportive of the complainant’s claim that storm damage occurred on 11 April 2021.
The letter by N dated 22 November 2024 was based on an inspection of the complainant’s home. N stated in response to M’s Report:
Whilst the box gutter does appear to be undersized it does not support the concluded findings that the roof is experiencing ongoing and long term water entry.
When inspecting the property this morning, it was cool and there was dew on the roof. Inside was warm with the heater running and around 20 degrees.
We completed attached thermal imaging scans and took moisture scans. Thermal imaging scans showed consistent images with expected cold spots around speakers and down lights. There were no black spots or leaks detected.
We took 16 moisture readings across the ceiling and bulk head (the main leak location). The average reading was 2.71% with a high of 7%. Readings of around 25% or more are what we would expect when water ingress is present. A test of the external wall was 7.6 and well within normal range.
After taking these initial readings we completed the survey of roof fall [which concluded that the roof has fall between 1- 1.3 degree’s with an average of 1.122]. We then water tested the roof with a hose noting that the water drained well with no pooling or water holding across the roof.
After this we completed a further 22 moisture readings across the ceiling and bulk heads with consistently low readings averaging 3.48%.
Long term water entry does not present moisture readings in this range. It is widely accepted that moisture readings of up to 15% are commonly found on external wall and ceiling linings where leaks are not present.
The recorded moisture readings, roof fall assessment and water testing show conclusive data that contrary to the MCS 97459 report there can’t be “long term water entry and leaks” and “ongoing water entry”. The roof has not been replaced and the above testing shows no evidence of this claim.
The letter from N dated 22 November 2024 was prepared over 3 and ½ years after the claimed storm event on 11 April 201. N did not provide an opinion that supports the conclusion that a single storm event caused the damage to the complainant’s property. The letter sought to respond to the conclusion in the report by M. However, it did not seek to respond to the conclusions in the reports by S and H which are set out in detail above.
Complainant has not established a valid claim
Based on the information provided, the complainant has not established a valid claim. The insurer’s reports (set out in detail above, principally those by S and H) are persuasive both in relation to the conclusions reached by those experts and having been prepared closer in time to the claimed damage on 11 April 2021. The reports by S and H are to be preferred to the complainant’s experts’ letters.
S’s conclusions regarding the cause of the damage were:
there was no evidence of any storm damage to the roof
all the internal damage had been caused over a long period of time due to a combination of maintenance issues and building defects only
there is no sisalation paper underneath the roof sheets and, as a result of this, condensation water had been dripping into the ceiling space over several years and had caused a large extent of the damage found
the top apron flashing was under size and did not comply with Australian standards. As a result of this wind driven rain had been blown up and over the tops of the roof sheets into the ceiling space where it has spread across the ceiling and has contributed to the damage
the silicone seals around the heating flue have signs of deterioration where further water can now seep through into the ceiling space and be another contributing factor
a combination of these issues had caused the damage
S’s conclusions were consistent with H’s conclusions regarding the cause of the damage:
points of un-weatherproofed areas and failed sealing attempts which allowed water to enter the roof through wind-driven rain and capillary action
evidence of a blocked roof gutter and water ponding at the roof gutter which allowed water to overflow from the gutter and enter into the roof cavity
the water ingress that had occurred and damaged the ceiling was a direct result of rainfall that was able to enter the house through gaps in the roof through various rainfall periods
water had entered the roof cavity due to the poor condition of the roofing causing the observed water staining during rainfall events
water ingress was attributed to a lack of effective maintenance/moisture protection over a prolonged period
the roof had sustained long-term deterioration and subsequent ingress issues in many locations before the recent event as evidenced by previous repair attempts
the damage is not attributable to the isolated event
Accordingly, the insurer was entitled to deny the claim as the complainant had not established a valid claim for storm damage on 11 April 2021.
The insurer also said on 5 March 2024 that it was entitled to deny the claim based on policy exclusions, including blocked gutters and limitations in the roof’s design and construction. As the complainant has not established a valid claim, it is not necessary in this Determination to consider whether or not the policy exclusions also applied.
Is the complainant entitled to non-financial loss compensation?
Yes. In the circumstances, an award of non-financial loss compensation is warranted.
AFCA can award compensation for non-financial loss
Under our Rules, AFCA can award up to $5,400 compensation for non-financial loss for a complaint made to AFCA on 29 October 2023. This must relate to poor claims handling or other actions of the insurer which cause an unusual degree of stress, delay, or inconvenience.
AFCA takes a conservative approach to compensation for non-financial loss. We expect complainants to be moderately robust, and we will not award compensation for the ordinary degree of inconvenience involved in making a claim.
Non-financial loss compensation is payable by the insurer
The insurer did offer non-financial loss compensation on $1,000 on 30 November 2023 and acknowledged that the complainant’s ‘claim and its outcome [had] been subject to several revisions, resulting in a protracted experience’. Based on the information, the complainant has experienced an unusual degree of stress, delay and inconvenience in the insurer’s handling of the claim. The claim has been under consideration by the insurer since April 2021 and there have been further delays in the consideration of the claim since the insurer’s offer of $1,000 on 30 November 2023. The insurer initially denied the claim and then sought to reconsider it after an earlier complaint to AFCA. Accordingly, an award of non-financial loss compensation is warranted and it is fair that the insurer pay $2,000 to the complainant.
Why is the outcome fair?
The outcome is fair because the insurer is entitled to rely upon the exchanged material and the terms and conditions of the policy to determine its obligations regarding the claim.
Supporting information
The AFCA process
AFCA’s approach is based on fairness
AFCA has determined this complaint based on what is fair in all the circumstances, having regard to:
the legal principles
applicable industry codes or guidance
good industry practice
previous decisions of AFCA or its predecessor schemes (which are not binding).
The respective parties have completed a full exchange of the relevant information, and each party has had the opportunity to address any issues raised. We have reviewed and considered all of the information the parties have provided.
While the parties have raised a number of issues in their submissions, we have restricted this determination to the issues that are relevant to the outcome.
We assess complaints on available information and circumstances
AFCA is not a court of law. We do not have the power to take or test evidence on oath, or to require third parties to give evidence.
When we assess complaints, we consider:
available documents
the recollections of the parties
all relevant circumstances.
We give more weight to documents created at the time the events occurred. If there are no relevant documents, we will decide what most likely occurred based on the available information.
If there are conflicting recollections and these are evenly weighted, we may find that a claim cannot be established.
Coded fields were extracted from the text by a language model and may contain errors. The published PDF is the authoritative record.