Refusal to treat refrigeration condenser failure as accidental damage, and business interruption denial
Text of the determination
Determination
|
Case number
|
12-00-1029359
|
Financial firm
|
QBE Insurance (Australia) Limited
Case number: 12-00-1029359 20 November 2024
Determination overview
Complaint
The complainant is the director of a business holding a Business Pack Insurance policy with the financial firm (the insurer). In December 2022, the complainant lodged a claim on the policy when the outdoor refrigeration condenser unit (the condenser unit) for the freezer room caught fire and ceased working.
The insurer has accepted the claim under ‘Machinery Breakdown’ cover section. It has paid the complainant the sum insured of $7,500 for the condenser unit and the sum insured of $20,000 for deterioration of stock, less policy excess of $500.
The complainant disputes this and says that the claim should be accepted as ‘accidental damage’. The complainant claims for loss of contents, business interruption and cost to replace the condenser unit.
For the sake of brevity, the complainant, the insured business, and the complainant’s representative will be referred to in this determination as ‘the complainant’ and ‘him’.
Issues and key findings
Has the insurer correctly assessed its liability?
No. Based on the available information, the panel is satisfied that the claim falls within the machinery breakdown cover. However, the insurer should increase its settlement to include the extra cover of inflation costs and repairs costs if the insurer has not already done so.
Is the insurer required to pay business interruption costs?
No. The policy does not respond to business interruption costs under cover for machinery breakdown.
Why is the outcome fair?
The outcome is fair as the available information establishes that the claim falls under the machinery breakdown cover. It would not be fair to require the insurer to pay the claim under business property or business interruption in circumstances where the policy does not respond. However, it is fair that the insurer pays the complainant for the extra cover as provided under the machinery breakdown.
Determination
This determination is in favour of the insurer.
Should the complainant accept the determination, within 14 days of receiving written notice of acceptance, the insurer is to:
if not already paid, pay the complainant under the machinery breakdown coverage section up to the sum insured of $7,500 (less excess $500) and for the deterioration of stock of $20,000 (less excess of $500)
pay the extra cover of inflation protection on the sum insured of $7,500 calculated up to 28 December 2022
pay the complainant the extra cover repair costs of $5,000.
Reasons for determination
Has the insurer correctly assessed its liability?
No. Based on the available information, the panel is satisfied that the claim falls within the machinery breakdown cover. However, the insurer should increase its settlement to include the extra cover of inflation costs and repairs costs if the insurer has not already done so.
Onus on complainant to establish a claimable loss
The complainant is required to show, on the balance of probabilities (that is more likely than not), that it suffered a claimable loss under the policy. This means that it must show the loss was caused by a risk for which it is insured.
Once the complainant, on balance, establishes a claimable loss, the insurer is liable for the loss unless it shows an exclusion or limiting condition applies. The insurer has the onus of proving, on balance, the application of the exclusion or condition.
The complainant says that the condenser unit was damaged after a contractor stood on it when he was replacing the gutters of the building. The complainant says that the impact to the condenser unit’s top caused the internal pipes to crush, causing a gas leak and ultimately the condenser unit to catch fire and require replacement.
The parties do not dispute that the condenser unit has failed. However, the insurer says that condenser unit’s failure was not from the impact but the failure of the silver solder, which had been used in a prior repair.
The policy provides cover for machinery breakdown as defined in policy
The policy provides cover for machinery breakdown. The policy defines breakdown as:
A sudden and accidental failure of machinery resulting in physical damage to the equipment which requires the repair or replacement of the equipment or a part of the equipment.
Breakdown does not mean:
depletion, deterioration, corrosion or erosion of material;
wear and tear;
vibration or misalignment;
the functioning of any safety device or protective device;
the failure of a structure or foundation supporting the equipment or a part of the equipment.
The available information shows the condenser unit was experiencing a leak
There are several service reports which confirm that the condenser unit was leaking refrigerant which required it to be replaced. This meant the condenser unit was not operating properly.
The service reports and the correspondence from the attending technician, CT state that on 26 September 2022:
it was unable to locate a leak
oil was covering most of the condenser unit
unable to tell if recent or past repairs
condenser fan coil deteriorated/broken
added refrigerant to system as it was slightly low.
On 27 November 2022, CT found:
system short on refrigerant
leak was found on condenser coil at end plate
will require reclaim unit and bottle to attempt repair.
On 29 November 2022, CT found:
leak and reclaimed unit
fixed leak
thoroughly cleaned unit and chemical cleaned coil
re-gassed unit and ensured system working well prior to departure.
CT provided an invoice dated 19 December 2022 which stated that it had attended on three occasions:
in relation to the damage caused to the freezers condenser unit due to the impact on the refrigeration pipes as a result of someone standing on the system.
CT noted one leak was found in the top of the condenser unit and has been repaired. However, believed that there was another smaller leak. CT says that because of the system running continuously at hot temperatures for an extended period, the condenser unit had sustained considerable wear and tear and would be unlikely to operate to its fullest function again.
Complainant says damage is caused by impact
The complainant says:
he observed a contractor had placed a plank on top of the condenser unit and had been walking along this when replacing the building’s gutters
this was in or around late June 2022
two weeks later he noticed oil leaking from the condenser unit and the guard around the fan appeared to be broken
he engaged CT to undertake repairs
after leak found and repaired, had to run condenser continuously for 72 hours to bring the temperature back down
since repaired, condenser struggled to bring the temperature down during the day
the damage was from the impact caused by the contractor
the claim should be assessed under the Property Damage section.
The complainant has provided photographs which he says show damage to the pipes directly under the housing of the condenser where the pipe and fan blades have been compressed due to downward pressure.
He says that the repairs were only undertaken as a temporary fix to allow him to trade over the Christmas period. However, the condenser unit failed on 28 December 2022. The complainant lodged the claim with the insurer on 22 December 2022 and provided a quote for the condenser unit’s replacement.
Insurer has obtained an expert report
The insurer appointed an assessor, S to attend and provide a report to the insurer. S has provided several reports. S attended on 17 January 2023 and noted that the failure of the condenser unit had resulted in loss of frozen stock.
In a report dated 13 February 2023, S noted that it was possible that the roofing contractor had placed planks on the outdoor condenser unit which have caused the refrigerant to leak. However, as the condenser unit was some years old and located close to the ocean, it was quite likely that the refrigerant leaks have been caused by corroded copper pipes within the condenser unit.
The insurer obtained a forensic metallurgist (FS) to assess the damage to the condenser unit. FS provided a report dated 20 February 2023. FS attended and inspected the condenser unit which was partially disassembled. FS found:
The top cover rested on a frame member and there was a clearance of 6mm between the top cover and the heat exchanger. There was no indication that there had been contact between the two even at the site of the bend.
FS says that the tube would have been subject to buckling once the end plate had been cut away to effect repairs. FS believed that the damage had most likely occurred during the repair while manipulating the tube to gain access.
FS also observed where one of the heat exchanger tubes had been repaired by silver solder. The repair was noted to be located near the end plate. A section of this heat exchanger was cut and analysed.
FS found:
The original silver soldered joint had apparently failed and the joint had subsequently been reinstated by the repair procedure in which new silver solder had been introduced to the joint.
FS also noted no evidence of corrosion or of fatigue cracking.
Insurer says cover for machinery breakdown only
Insurer says that the assessment found that the damage was not because of impact damage and therefore it does not fall under the property section. The insurer says that the complainant has not provided sufficient or substantial evidence to support the complainant’s theory on causation, and therefore the insurer is only able to consider the loss as anything other than machinery breakdown.
The insurer says that there have been ongoing issues with the refrigeration unit for 5 years. Further, the complainant completed temporary repairs prior to the submission of the claim.
The insurer says that the complainant has changed his version of the cause of the damage to the condenser unit: first impact, and now fire. The insurer says that the onus placed on the complainant for both causes has not been satisfied or established that a claim that could be considered under any other section of the policy but ‘Machinery Breakdown’.
Cover falls within machinery breakdown
The complainant’s version of events is not disputed by the insurer. However, the parties disagree whether the contractor caused the condenser unit to ultimately fail when he placed a plank on it.
Damage can have more than one cause. When deciding how the policy responds, the panel needs to identify what the proximate cause of the damage was. This is a question of fact depending on the circumstances. The proximate cause is not necessarily the first or last or the sole cause of the loss. It is the effective, dominant or operative cause of the loss.
While the complainant says that the damage is consistent with impact damage from the contractor, this is not supported by the expert opinion of FS. FS observed the dent in the cover, consistent with what the complainant had reported, however found that this was not located near the repaired pipe.
While CT noted in its report dated 19 December 2022 that the damage was due to impact damage, he does not explain the mechanics of how it caused the damage. The leak was found on the condenser coil end plate. Further, CT noted that the condenser fan had deteriorated and was broken but had not attributed this to the impact damage.
The panel is not satisfied that the absence of metal fatigue or corrosion as noted by FS supports that the condenser unit was damaged by impact as claimed by the complainant.
The panel acknowledges that FS did not have the benefit of examining the original silver solder. However, the opinion from FS that the condenser unit’s silver solder failed and caused the leak is supported by an analysis of the entire condenser unit and the condenser coil. The photographs provided by FS also support a logical explanation of the damage. FS concluded that the heat exchange tube was not subject to sustaining loads and therefore was not the result of an impact.
The panel is satisfied that the proximate damage to the condenser unit is because of the failure of the silver solder. This meets the definition of machinery breakdown and cover falls within this section of the policy.
The panel notes the complainant’s concerns that he was prejudiced and unable to obtain an expert report as the insurer has since disposed of the sample. However, the panel notes that page 17 of the PDS provides cover for physical loss or damage to insured property but does not cover theft or breakdown of the property insured.
That is, the panel is satisfied that the complainant is not otherwise prejudiced by the disposal of the sample as it does not otherwise entitle him to further cover under the policy.
The COI confirms that under the Machinery Breakdown cover section, the sum insured is $7,500 for each item (blanket cover for 10 items) and the sum insured for deterioration of stock is $20,000. The panel is satisfied that the insurer has correctly paid these sums to the complainant under the terms of the policy.
Policy includes extra covers
Page 60 of the PDS provides that, if a claim is paid under the policy for breakdown of machinery, it will also pay or provide the extra cover for inflation protection and repair costs.
Inflation protection is defined as:
The sum insured on items of machinery shall at the time of loss be increased according to the consumer price index by the proportion which the number of days since the commencement of the period of insurance shall bear to the whole of such period.
The insurer is to apply this additional benefit to the sum insured of $7,500 and cash settle the complainant if it has not already done so.
The extra cover of repair costs provides:
The cost of consulting engineers’ fees (excluding fees for preparing a claim) necessarily incurred with our written consent (which consent shall not be unreasonably withheld), in the reinstatement of machinery. Provided that where the sum insured is exhausted, we will pay an additional amount of up to $5,000 in respect of this extra cover.
The complainant has provided a quote form CT for the replacement of the condenser unit. The condenser unit was $13,189 (plus GST) and other costs were noted which included the materials, refrigerant, labour and travel. These costs exceed $5,000.
The complainant says that the condensing unit was replaced on or around 19 January 2023.
The panel is satisfied that it is fair and reasonable that this additional cover of repair costs of $5,000 is paid to the complainant. This is because the sum insured has been exhausted and the complainant forwarded to the insurer a copy of the invoice when the claim was submitted.
Is the insurer required to pay business interruption costs?
No. The policy does not respond to business interruption costs under cover for machinery breakdown.
Policy provides cover for business interruption in certain circumstances
The complainant’s COI confirms cover for Business Interruption based on an annual revenue of $900,000. The COI confirms that the complainant had elected to insure contents under the business property section in the sum of $550,000.
Page 27 of the PDS provides cover in the event of business interruption as a consequence of damage during the period of insurance, to any property insured or any part thereof used by the insured at the premises for the purpose of the business.
Damage is defined on page 25 of the PDS as being:
Physical loss, destruction or damage occurring during the period of insurance caused by an event insured under the ‘Property damage’ cover section, the ‘Theft’ cover section, the ‘Money’ cover section, the ‘Glass’ cover section or the ‘General property’ cover section or ‘Goods in transit’ cover section.
As breakdown of property insured is not covered under the Business Property section (page 17 of the PDS), the Business Interruption cover has not been triggered.
Insurer entitled to deny Business Interruption claim
Upon review of the available information, the panel is satisfied, as noted above, that the claim falls under the Machinery Breakdown section of the policy.
It does not fall within the definition of ‘damage’ as defined under the Business Interruption section of the policy.
The panel is satisfied that the insurer is entitled to deny this portion of the claim and is not required to take any further action.
Why is the outcome fair?
The outcome is fair as the available information establishes that the claim falls under the machinery breakdown cover. It would not be fair to require the insurer to pay the claim under business property or business interruption in circumstances where the policy does not respond. However, it is fair that the insurer pays the complainant for the extra cover as provided under the machinery breakdown.
Supporting information
The AFCA process
AFCA’s approach is based on fairness
AFCA has determined this complaint based on what is fair in all the circumstances, having regard to:
the legal principles
applicable industry codes or guidance
good industry practice
previous decisions of AFCA or its predecessor schemes (which are not binding).
The respective parties have completed a full exchange of the relevant information, and each party has had the opportunity to address any issues raised. We have reviewed and considered all of the information the parties have provided.
While the parties have raised a number of issues in their submissions, we have restricted this determination to the issues that are relevant to the outcome.
A panel determined this matter
Due to the nature of this complaint, we referred it to a panel for determination. The panel includes:
an ombudsman
a member with significant experience in consumer and small business advocacy
a member with extensive experience in the insurance industry.
We assess complaints on available information and circumstances
AFCA is not a court of law. We do not have the power to take or test evidence on oath, or to require third parties to give evidence.
When we assess complaints, we consider:
available documents
the recollections of the parties
all relevant circumstances.
We give more weight to documents created at the time the events occurred. If there are no relevant documents, we will decide what most likely occurred based on the available information.
If there are conflicting recollections and these are evenly weighted, we may find that a claim cannot be established.
Coded fields were extracted from the text by a language model and may contain errors. The published PDF is the authoritative record.